Ok need advice.

Two domestic consumer units both fed of same Escos ideally should only have been one but she to it being an older house and the location of DNO equipment this was not possible without unreasonable expense. As both are beside each other and fed from same Escos could 1 SPD 2 in one consumer unit service the circuits on both boards???

Any help be appreciated.

J
 
Ok need advice.

Two domestic consumer units both fed of same Escos ideally should only have been one but she to it being an older house and the location of DNO equipment this was not possible without unreasonable expense. As both are beside each other and fed from same Escos could 1 SPD 2 in one consumer unit service the circuits on both boards???

Any help be appreciated.

J
One spd should benefit both.
 
What is the total length of cable between Lin at the isolator of the non-SPD board, via the SPD in the other board, to earth?
It's supposed to be less than 50cm.
I suspect your suggestion might result in less protection for the second board.
The boards are literally beside each other. Maybe a difference of 10/15 cm tails from same Henley Blocks. DNO is NIE (Northern Ireland) wanted to charge 300 quid to move the meter and head.
 
The boards are literally beside each other. Maybe a difference of 10/15 cm tails from same Henley Blocks.
Just to emphasise the 50cm 'rule' I was talking about, some theory below. A surge is shunted to earth, so the length of the earth connection used is part of the calculation. So distance of Lin of second CU to Lin of first CU (if that's where the SPD is going), plus distance from Lin to MCB protecting SPD, plus distance MCB out to SPD, plus distance from SPD earth terminal to main earth bond. All those added together is supposed to be less than 50cm, and if it is that, the household could still get a 500V surge on top of the mains voltage (strictly on top of the SPD cut-in voltage)!


IMG_0745.jpeg
 
Just to emphasise the 50cm 'rule' I was talking about, some theory below. A surge is shunted to earth, so the length of the earth connection used is part of the calculation. So distance of Lin of second CU to Lin of first CU (if that's where the SPD is going), plus distance from Lin to MCB protecting SPD, plus distance MCB out to SPD, plus distance from SPD earth terminal to main earth bond. All those added together is supposed to be less than 50cm, and if it is that, the household could still get a 500V surge on top of the mains voltage (strictly on top of the SPD cut-in voltage)!


View attachment 118111
Regulation 534.4.8 SPD installation shall
preferably not exceed 0.5m and in no
case exceed 1m
 

Reply to SPD2 in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

If two tariffs are sufficient, and you don't need too many ways, you can easily add an SPD kit to the Fusebox F2014DT dual tariff board. The only...
Replies
1
Views
208
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
1K
I've seen a few posts here which tend to suggest that wiring in a motorhome (or caravan) wouldn't be subject to normal inspection rules, but even...
Replies
0
Views
289
  • Question
The norm is that it goes from the DSO (ESB) fuse to a DSO isolator with a contractor's side, and then to the main overcurrent device. The ESB...
Replies
9
Views
3K
  • Question
Could someone kindly share why the SPD unit must be in parallel? I'm confused sorry! Hard to say without a basic wiring diagram of the current...
Replies
21
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks