catdog
I'm no expert on split concentric (assuming that's what this is)......But an earth clamp doesn't seem the best solution to this (also as the earth cores appear to be insulated!
This is for an eicr on a sub main but I'll have to do the remedial work at some stage.
Any advice on how to terminate this correctly?
Thanks!
[ElectriciansForums.net] Split Concentric Termination
Not aware of any requirement in BS7671 to provide mechanical protection to cables buried in the ground?
NBP is presumably referring to 522.8.10 where cables without an incorporated, cpc suitable, earthed covering should be protected against mechanical damage by a conduit or duct.
Even though the regulation is worded with reverse emphasis.
I agree, concentric is live centre conductor and pen outside conductor. Split concentric is live centre and split outer earth and neutral separate, not seen it with swa but that's not to say it doesn't exist!
The Neutral is connected to earth.
The neutral is sleeved/insulated
If it wasn’t then it is effectively a PEN conductor which split concentric is not and therefore can’t be used in the consumers installation.
It’s split concentric cable being discussed here the neutral and earth are separated hence the name split
Reply to Split Concentric Termination in the UK Electrical Forum area at ElectriciansForums.net
I tend to write the circuit number on the mcb say every 5th mcb/rcbo just to help make it easier to locate in a large multi way or 3ph board...
I think a 3 legged breakout boot would be your best bet in the circumstances.