Spot the electrical crime committed at approximately 8:45 in this video.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Spot the electrical crime in the UK Electrical Forum area at ElectriciansForums.net
corrected that bit for you. bonding relates to extraneous parts. sorry to be pedantic.I can follow that argument when say a socket face is attached, as the socket earth is connected to a metal bush that the screw sits in, thusbondingearthing the screws and back box.
however this is not the case for most light switches and blank plates.
except grid switches.
I hate this.. its rough. I'm pretty sure there is stupid regulation that state as long as the surface area is less than a certain CSA it doesn't require earthing as long as it is RCD protected.
I'm going to try and find it now ?
410.3.9
Bullet point (iii)
I would post it but that would be illegal and against forum rules.
Cobblers. a single back box is > 50mm x 50mm, the screws can come into contact with a person. and you can't say that a connection would be difficult.410.3.9
Bullet point (iii)
I would post it but that would be illegal and against forum rules.
Completely agree, its bad workmanship.hmmm, maybe.
if the back box is not accessable.
but you have to admit it is wrong/poor work?
Back box not earthed?
Spot the electrical crime committed at approximately 8:45 in this video.
The point is that the screws can’t be gripped and can’t make any significant contact with the human body other than a finger tip, the back box can’t be touched at all.Cobblers. a single back box is > 50mm x 50mm, the screws can come into contact with a person. and you can't say that a connection would be difficult.
Well that's today's school day moment for me. Wasn't aware of that one.410.3.9
Bullet point (iii)
I would post it but that would be illegal and against forum rules ?
Says the same thing in the 18th edition gn1 and gn8I must admit that my version of GN1 is the 17th Edition Amendment No. 3 version rather than the 18th Edition version, however it states:
"However, the IET takes the view that flush metal accessory boxes should be considered to be exposed-conductive-parts and connected to the main earthing terminal by means of a circuit protective conductor."
So regardless of what any Regulation states about screw heads the actual backbox still must be considered to be an exposed-conductive-part, which was my point.
Reply to Spot the electrical crime in the UK Electrical Forum area at ElectriciansForums.net