Spot The Mistake | Page 2 | on ElectriciansForums
Discuss Spot The Mistake in the Australia area at ElectriciansForums.net
telectrix
Mentor
Nearly Esteemed
cheshire/staffordshire
yea jonny but still quote it as its NOT Ideal and NOT accessible and breaking the law to pull it
Grimmy Im hard on PIRs not every fault JUMPS out at you but if you "miss" something thats the thing that may come bite your BUM in the future
No cover on consumer unit. Disgraceful.lol
Live labelled as neutral. Earth looks too small
ive just noticed the earth bar? or lack of a decent 1. the main earth looks small too. Also the boards are missing the covers!! the live from the meter to the henley is labelled as a neutral.
As it looks like a TN-S supply why would the main earth conductor be automatically to small?
Still would change it on a CU change to a G/Y.
I thought it was a TN-C-S because of the connector that looks like its entering the SH right next to the neutral? But then I was confused because the cable then looked like it went down and was connected TN-S style??
If it is TN-S, what is the purpose of the connector on the side of the SH?
Cheers
Ok, having thought about it, I presume that if it was TN-C-S the earth would enter the SH completely, and that having a connector exposed like that would be extremely dangerous :behead:
Normally if it's PME you get a sicker, but agree that could have been removed or not put on altogether.
To me it looks a TN-S as there is a cable attached to the lead sheath, it may have been TN-S at one stage and then converted to PME and they never removed the the original TN-S link, but if it was done as a recent thing I would have thought they would have used G/Y cable.
Only person who knows for sure is the Tel
the connector on side of the head is the termination of the TN-S earth bar from the cable sheath. the "spare " cable going down is to an earth rod. found this arrangement on a few 60's installs. (belt & braces?). it's all done now. 10mm main earth ( caclulated using adiabatic ) and a nice shiny new MET. new starbreaker 13 way CU. you may be interested to know i found a new variation on the dreaded borrowed neutral. fluorescent light in garage ( one of three ) on 2 way switch, L coming from 2 way switching, N was supplied direct from CU neutral bar with a length of 1.0mm T/E with the red cut off. also, some clown had split the rfc to add sockets and left as 2 radials on a 30A 3036. this left me with needing an extra way, which i only had on the unprotected section of the new CU, so had to fork out for an RCBO, ÂŁ30, customer was happy for me to add this to bill, so all cushty.
Did a supply change over only a couple of weeks ago where the permisses were on a shared supply that was subsequently split with the addition of a new incommer for the second business. I go in to have a look between the supply head being installed and the metering being fitted to find a bare piece of copper going from the PME block out to a plastic enclosed MET. I duly leave a nice length of 16mm earth cable and a note for it to be fitted. Return 2 weeks later to find the copper wrapped in tape and my note scribbled with "not my job mate"...........
But would a TN-C-S arrangement like that be acceptable? I just assumed that because N is considered a live conductor, that it would not be acceptable or safe to have a connection like that that could be touched?
Cheers
Cheers
Remember the link for the NEUTRAL/EARTH connection is 99% of the time in a TNC-S system done in the head, and often you will get in older heads just as above an extended earth bar open just like that. Like attached
View attachment Lucy HRC Insulated House Service Cutouts.pdf
yep, similar but not as ancient. i think that around the early 70's heads were supplied with the block attached in readiness for PME, but no link across to the neutral in the head. the way to be certain is to measure the pssc and pefc. if the readings are identical, then its TNC-S. if the pefc is lower than the pssc, then it's TN-S.
Reply to Spot The Mistake in the Australia area at ElectriciansForums.net
Your biggest mistake is admitting to a mistake.... If theres no witnesses, it didn't happen. However.... A few golden rules.... Never trust...
That'd be a great help mate. You could attempt to use chat gpt. Instruct it to rewrite the following and paste the lot in and 50% of the time it's...