Washing machine and dishwasher if on at the same time and heating water can be around 4-5kW as both have similar heating elements.
 
Nothing at all wrong with a radial. aslong as you install 4mm2 cable protected by a 32amp in the kitchen. 20amp with 2.5mm2 cable serving the bedrooms and another 20amp radial for downstairs.

Easier to 1st fix(no return to c-unit).Easier and quicker to test.Easier to fault find.Less cables in fuse box to 2nd fix. I think its the way forward. Some sparks cant see past the "ring final circuit".

Obviously i do still install rings but im leaning loads more to a radial circuit. My NAPIT assesor put me on to the idea "why u still messing around with rings" i quote.

Only for electricians that are ignorant of the benefits and adaptability of Final ring circuits. You design a circuit of any description based on the needs and requirements of the situation, taking possible future needs/requirements into consideration....
 
I seem to remember that you could only do this within 50sq/m, where a ring could be in 100sq/m, so correct me if i'm wrong, i'm getting old and forget things real quick.
 
I believe the uk is one of the only countries to use a ring circuit. The reason been is when you cut through the cable you have two radials running off the wrong mcb. You might not beable to cover such a large area using radials but at least you dont have a problem spuring off.
 
I tend to use radials where appropriate for 'house' circuits, and RFC's for kitchens, utilities etc.

I just can't see why (in a properly designed circuit) a flat screen telly needs to be provided with 5mm2 of copper. But a kitchen, that's a different matter.

Floor area/csa/rating considerations taken into account, there's no more flexibility in a ring than a radial, it's just an economic argument on loading as to whether it's cheaper/more eco friendly to run the whole circuit in 4mm or just need to run a return leg (let's face it, not normally that long) in 2.5mm.
 
i agree england is the only country to use a ring circuit invented because of the war. there is already talk of doing away with the ring curcuit so that once again we can fall in line with our european bretherin
 
As far as I'm aware, the OP's intention is to spur off of a Radial , not a RFC.
As for there being talk about doing away with RFCs, there has been talk about such ever since they were introduced.
The IET has no intention of doing away with RFCs, and considering the current high price of copper, it is more likely that other countries will be introducing RFCs themselves
 

Reply to Spur for diswasher and washing machine in radial circuit in the Electrical Appliances & Whitegoods Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
511
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
754
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

K
  • Question
Ah, I see. The op question is ambiguous, and I took it that he wanted to add a socket for a washing machine from and exiting switch fused spur. A...
Replies
10
Views
1K
You may still have a problem with earth leakage though, it could be that the Samsung has less leakage than the Bosch ones. If you do get a random...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top