Just wondering if I got this right but is it ok to take a 2.5mm spur from a 32MCB ring main Or should I use 4mm cable.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Spur from 32MCB in the UK Electrical Forum area at ElectriciansForums.net
What Spoon saidHave a look at Appendix 15 of the BBB (Page 505)
Have a look at Appendix 15 of the BBB (Page 505)
Appendix 15 should ex[plain it all, a good read is required.Yeah my other thoughts were to just ad a 20MCB with a 2.5mm radial for 1 socket.
Sorry, explain pleaseThe 2.5mm the spur is made with has an advantage ,
it is not evolved in the current flowing thru the rest of the ring .
(that may already be well loaded)
(Tin hat in place)Sorry, explain please
Your spur will not require overload protection as long as the load can not exceed the Iz of the spur cable so at most you can only have a max load of 26 amps from one double socket which is highly unlikely that that is what will be used.I think 4mm is more suited as Iz has to be higher than In.
You could, but that is a new circuit with the need to notify the work to the local authority. Not worth the PITA.Yeah my other thoughts were to just ad a 20MCB with a 2.5mm radial for 1 socket.