Hi chaps...

Been asked to add a light in an under-stairs cupboard.

A spur from the downstairs socket circuit runs through that cupboard to a double 13A outlet in the kitchen. I'd like to tap into that for the light, but under the regs I'd have to fuse it down first.

The thing is, the 2.5mm T+E used is rated for 27A (in this case, method C). Worse case scenario is that both those sockets are used at 13A, so that's 26A being drawn.

The light which is going to be fitted is a very low energy LED fitting, so uses next to nothing. If the light is on and the sockets are used, the maximum that could be drawn through the spur is only ever so slightly over 26A, so the cable is still not overloaded.

Would anyone NOT fuse the spur in this instance (as it's clearly not a risk), or should it be done anyway as per the regs (and have the inconvenience of the blown 13A fuse if the toaster and kettle are used together)
 
Cheers for the help guys,

If I decide not to fuse the spur and work on the fact that the calculations show the cable is adequate for the 26A + the light, should I just note it on the Minor works certificate and be done with it? I wouldnt be recording on a certificate work that i know damn well doesnt comply , you're just leaving yourself open for a kicking if it all goes pete tong.

Realistically if I fuse down the whole spur, the chances of it blowing are pretty much nil, but it just seems a bit pointless if the cable is always going to be fine. it doesnt matter if the cable is 95mm - standard circuit arrangements limit 1 unfused connection point for each spur.

Being an understairs cupboard it's not like anyone will be changing the simple pendant for a fancy 5x100w bulb chandelier or anything! very true , but we all know you're trying to justify a design decision that just isnt right.

what are the chances of this kitchen socket using more than 13a after being fuse down ?
what is being plugged into this socket now ?
if very little then just fit the extra fcu and stop dithering ;-)
 
Last edited by a moderator:
Have I read this wrong or are you saying that the total for a double socket-outlet is 26A and not 13A?

- - - Updated - - -

Have I read this wrong or are you saying that the total for a double socket-outlet is 26A and not 13A?
 
I just can't understand why a FCU is being tried to be left out. Surely as per the regs (although I'm qualified spark - I am still learning and happy to receive advice) a FCU is required??!
But on a side note surely you would want to switch the light off?? The method you plan to use would mean your light would be on 24/7!!
I would much prefer to fit a FCU as you'd get protection, discrimination and also a means to switch on and off.
 
The method you plan to use would mean your light would be on 24/7!!

How on earth do you work that out?!

Why on earth would I fit an unswitched light fitting?!

I was just curious about the regs regarding spurs as I was planning on adding a tiny load to a spur, which could only ever draw 26A or less and which was capable of taking 27.5A.

It seems that on this occasion the regulations are too restrictive... The 2.5mm T+E cable is capable of carrying the worst case scenario load of the double sockets, plus the maximum that could be draw by my addition of a light fitting. I just don't get why the regs insist on fusing in this case, when it would restrict the cable to less than half its capacity.

I know the regs are there to stop idiots chaining multiple double sockets from a single spur, I just don't see why there isn't something which allow the sparks to do the calculations and make the decision for themselves!
 
Thinking about it, ANY spur on a normal (I mean, 30-32 Amp protected) ring final isn't really very safe according to the regulations...

A single run of 2.5mm T+E can take 27.5 amps maximum... Seeing as most RFCs are protected by a 32A mcb or 30A fuse, it means in the event of a wiring fault the spur could be overloaded with no trip!

A 2.5mm radial on a 32A mcb wouldn't comply with the regs, so why does a 2.5mm spur from a ring final? Is this the only time when an mcb does NOT have to protect the cable in a worst case scenario? If so, why?!
 
Thinking about it, ANY spur on a normal (I mean, 30-32 Amp protected) ring final isn't really very safe according to the regulations...

A single run of 2.5mm T+E can take 27.5 amps maximum... Seeing as most RFCs are protected by a 32A mcb or 30A fuse, it means in the event of a wiring fault the spur could be overloaded with no trip!

A 2.5mm radial on a 32A mcb wouldn't comply with the regs, so why does a 2.5mm spur from a ring final? Is this the only time when an mcb does NOT have to protect the cable in a worst case scenario? If so, why?!

Hence why only one spur is allowed, therefore meaning even a double socket with 2 kettles in could pull 26A! The socket would give uip first!
 
The difference between a spur and a radial on 2.5mm is, a spur = 1 double socket (max 26A), a radial many double sockets @ potentially 26A each.

The fuse in the plug/s protects the cable for the spur, which as SS said above, is why you are only allowed the one.
 
Last edited:
With regard to spurs,
I seem to remeber someone on here putting it that -
Your Short circuit protection is provided by the 32A MCB
Your overcurrent protection is protected by the bs1362 fuse.

So is wiring a 2.5mm radial to 1 Socket protected by a 32A MCB O.K. as well :cool3:
 

Reply to Spur from a spur? Theoretical reason for it being allowed... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K
  • Question
Thanks for the input guys. Lighting track is out of the question. The routing (h section guirders and angle iron) means that swa cable clipped...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top