Spur from Ring Final Circuit | Page 3 | on ElectriciansForums

Discuss Spur from Ring Final Circuit in the DIY Electrical Advice area at ElectriciansForums.net

Just before I go, if your changing a light fitting you just need to confirm the voltage and the integrity of the earthing (Earth loop Impedance) and that the circuit has no obvious issues like an incorrect OCPD etc, if however you are extending, altering or wiring new then a full test of the circuit is required and any of your work has to meet BS7671 regardless of whether the rest of the circuit does.
 
So when you change a light you have to do an insulation resistance test? So you would have to remove all the light bulbs on the whole circuit and do the test, just cos u changed a light?

If changing a light fitting like for like then it is reasonably accepted you are not altering the circuit and therefore this testing is not required and neither is a certificate. This doesn't mean that no testing takes place ever in this instance though. Verification of a valid earth path while putting up a metal fitting for example.

If you are adding an extra light point into a circuit the regs asks that you:
Ascertain that the installation is in a safe condition to perform the alteration on and is suitable for the alteration, this includes earthing and bonding.
Ensure the work complies with the regulations
Inspect and test your work and produce a certificate.

Strictly, the work you are doing is the only part of the circuit that would need its test results recording on the test certificate. In practice values for the whole circuit are commonly recorded and are also acceptable. You have to, after all, verify that the existing installation is suitable for the alteration.
 
Also RCD tests where relevant.
I would suggest that if you will be bringing in a skilled person to test your work that you arrange this prior to carrying out any more work. Whoever is signing the certificate may wish to stipulate design and installation methods, such as connections to ring circuits, and wish to see the installed cables at first fix stage.

Thank you for taking time to read the section on testing and certification. Although BS7671 is not a statutory document, it can be referred to in a court of law, by insurers, and by solicitors during house sales etc. It is good sense to get all work properly tested and certificated as evidence of safety.

Thank you for your advice. I am doing a course with a company called Trades Gateway. You study at home using course material and online and have a tutor. I take tutor marked assessments after each module and after so many modules you do two weeks at college and take exams. I am due for my 1st two weeks at college starting Monday. 1st week is on health and safety and 2nd week is inspection and testing. So hopefully in 2 weeks time I will be able to test it myself if I pass the exam. I have a multi function tester, just gotta get it calibrated
 
Just before I go, if your changing a light fitting you just need to confirm the voltage and the integrity of the earthing (Earth loop Impedance) and that the circuit has no obvious issues like an incorrect OCPD etc, if however you are extending, altering or wiring new then a full test of the circuit is required and any of your work has to meet BS7671 regardless of whether the rest of the circuit does.

Thank you
 
My last thread was taken down due to copyright reasons, I think it was because I scanned a page from the wiring regs and posted it.

Can anyone tell me if this circuit design conforms to regs?

View attachment 34318
Are the 2 JBs MF? if not are they accessible?
 
In the thread that got deleted, didn't you say you were considering this option because the builders had been in and put down a tiled floor? If this is correct and the work is under the remit of building control, it may be prudent to check up on the certification requirements of LABC so that the home owner can get a completion certificate.

As for getting somebody else to test and sign off - good luck with that one!
 
Gigsy, you state that BS7671 isn't law, however, the Electricity at Work Regulations are law. Have a look at Regulation 4 of the EAW Regs - now it doesn't explicitly state that inspection and testing are required, however, if you think about it inspection and testing are absolutely required to ensure you comply with this regulation. Without inspection and testing how else are you able to prove that systems are safe etc?
 
Gigsy, you state that BS7671 isn't law, however, the Electricity at Work Regulations are law. Have a look at Regulation 4 of the EAW Regs - now it doesn't explicitly state that inspection and testing are required, however, if you think about it inspection and testing are absolutely required to ensure you comply with this regulation. Without inspection and testing how else are you able to prove that systems are safe etc?
As the title says Work, it does not apply to domestic situations.
 
As the title says Work, it does not apply to domestic situations.

So is there no legal requirement for electrical safety at home? Anything goes?
 
Tosh. Work doesn't mean the location, it means the activity. As in doing work on the electrics.
I probably didn't make it too clear I was understanding this is DIY query and that the op is not employed or being paid for these works, if this is the case E&WR 1989 do not apply. If I am incorrect in assuming this then they do.
 
Last edited:
It applies to employers,employed and self employed It dont matter whether the location is domestic or comercial/industrial
 
It applies to employers,employed and self employed It dont matter whether the location is domestic or comercial/industrial
What I am saying, if employed or being paid as self employed then it applies, if a DIYer then it doesn't.
 
In diy you can do anything unless it goes wrong or an insurance company/mortgage company or buyer requires a cert
 
In diy you can do anything unless it goes wrong or an insurance company/mortgage company or buyer requires a cert
Well if Cert is required then someone would be employed and it would apply.
 

Reply to Spur from Ring Final Circuit in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Well we called it a room, but it was only a hole in the ground covered with bit of canvas.
Replies
13
Views
650
An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
682

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top