Spur/Junction for outdoor socket for PHEV charging? | on ElectriciansForums

Discuss Spur/Junction for outdoor socket for PHEV charging? in the DIY Electrical Advice area at ElectriciansForums.net

Joined
Sep 19, 2024
Messages
7
Reaction score
0
Location
Grimsby
Hi all,
I have a hybrid car and I’m trying to install a socket outdoors. I’m on E7 and have storage heaters on their own circuits, can I make a little T junction within a back box like so and connect that round the corner to an external EV-rated socket? Circuit is 16A, storage heater does not get used, and the socket has RCBO protection. The switch is for the storage heater, cable from CU runs vertically down and powers only the storage heater.

Thanks in advance,
Rob

[ElectriciansForums.net] Spur/Junction for outdoor socket for PHEV charging?
 
TL;DR
Spur from heater circuit for EV socket
I would not do that install if a customer asked me to.

the heater has a look of a well used heater. not as you say one that is never used.
it may be that it was used in the past and now you don't use it but other people would not be aware that you cant use them both at the same time.

I would always recommend a proper EV charger instead of a glorified outdoor socket.
 
Are you sure that’s the switch for the heater? There’s no flex going between.

Your socket will only work at off peak hours…

Your socket, being outside, will need to be rcd protected. (All sockets should be, but especially for outside)

If the CU is close, get a proper charge point installed.
 
Are you sure that’s the switch for the heater? There’s no flex going between.

Your socket will only work at off peak hours…

Your socket, being outside, will need to be rcd protected. (All sockets should be, but especially for outside)

If the CU is close, get a proper charge point installed.
Yep, comes down from the CU to the switch which goes down and round the corner to the storage heater. Charging is 10A/230V max and only a 11.1kWh battery so no point getting a proper charge point, would take me longer than I have the car to pay off vs using petrol alone. Off peak charging is good anyway as it’s half the price
 
I would not do that install if a customer asked me to.

the heater has a look of a well used heater. not as you say one that is never used.
it may be that it was used in the past and now you don't use it but other people would not be aware that you cant use them both at the same time.

I would always recommend a proper EV charger instead of a glorified outdoor socket.
We don’t use it, people who had the house before did. As there’s only two of us in the house we’d know not to use both (heater is next to a door anyway we may as well pay to heat up the outside)
 
A mode 2 charger can be connected from another circuit but it is suggested this is only for occasional use otherwise it should be a dedicated circuit. If using a 13A socket it should be identified for EV charging by the manufacturer.
 
Does your landlord know you are doing this?
Has your landlord carried out an EICR and given you a copy as required by law.
 
Does your landlord know you are doing this?
Has your landlord carried out an EICR and given you a copy as required by law.
I asked him if I could get a socket installed he said yeah that’s fine. Got a quote from an electrician he said the CU isn’t up to code and an EICR hasn’t been done as it would show the CU needs replacing. Decided not to go with the electrician as he wanted to spur off a socket on the front ring and the internet says no to that
 
They are breaking the law not having an EICR carried out.
You can connect from the ring final but it would only be suitable for occasional use. How often do you plan on using it?
 

Reply to Spur/Junction for outdoor socket for PHEV charging? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

  • Question
Cheers guys, enjoyed reading all the responses. I'm an apprentice and it was a conversation that came up at work between two electricians...
2
Replies
43
Views
3K
  • Question
You can do ether, but obviously have to have the appropriate number of terminal holes to do so (5-way Wago as they don't make 4-way). However you...
Replies
24
Views
8K
If the spur in the lounge has a 13A fuse, and everything outside is protected by that fuse, then you can add what you like up to that 13A limit...
Replies
1
Views
4K
  • Question
You don't need one unless the buyer insists. What happens in reality though is this holds up the sale if the seller decides to make an issue of it...
Replies
67
Views
10K
Wire the socket up first, on a 13A spur, then the switching box. I'd avoid powering the socket via this switching box's 8A outlet. With the...
Replies
1
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks