New to site. After abit of advice.
Adding a 13 amp fused switched spur to a ring in 2.5 mm t&e, only the current wiring is in 2.5mm with 2.5mm cpc. Protected by a C32 RCBO 30mA , only the CPC is going to be mixed 1.5 and 2.5.
Can’t fined anything in regs book about mixing cpc. Any advice would be great.
New to site. After abit of advice.