spurs | Page 3 | on ElectriciansForums

Discuss spurs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Have a look at 'ring final circuit' definition in part 2 of BS 7671.......

As this is a caravan site lenny you have installed a distribution circuit reg 708 So you have wired the distribution circuit in a form of a ring.

But if it's a ring final circuit how did you manage to comply with reg 708.553.1.12 where it called for each socket to have an individual overcurrent device. As well as 708.553.1.13 individual for RCD protection.

I don't think Lenny you can get away with what you did as a fing final circuit mate.
 
Yes, the term 'final circuit' is 'the devil in the detail' and in my opinion is the difference between the 2 different types of ring.
 
As this is a caravan site lenny you have installed a distribution circuit reg 708 So you have wired the distribution circuit in a form of a ring.

But if it's a ring final circuit how did you manage to comply with reg 708.553.1.12 where it called for each socket to have an individual overcurrent device. As well as 708.553.1.13 individual for RCD protection.

I don't think Lenny you can get away with what you did as a fing final circuit mate.


i'm sure each caravan socket outlet will have separate rcbo
 
I don't think Lenny you can get away with what you did as a fing final circuit mate.

And I never said it was......just stimulating debate.;)


As you say a ring 'final' circuit or any type of 'final' circuit must be directly connected to current using equipment. The ring circuit I installed connects to overcurrent & earth fault protection devices, not directly to the socket outlet.

I've come across large factories & hospitals also have large ring circuits supplying secondary DB's, in the region of 800A or more.

Slightly off topic but relevant I felt.
 
And I never said it was......just stimulating debate.;)


As you say a ring 'final' circuit or any type of 'final' circuit must be directly connected to current using equipment. The ring circuit I installed connects to overcurrent & earth fault protection devices, not directly to the socket outlet.

I've come across large factories & hospitals also have large ring circuits supplying secondary DB's, in the region of 800A or more.

Slightly off topic but relevant I felt.

When I was at home I did a lot of work for a company near me .............the old blue pill maker ..............and they had a fantastic ring main system. Though it was the domain of the HV guys I did a lot with them. on the ATS side of things.

They had a about 20 odd transformers around the place and if they lost one the ATS system would reroute and restore power via the ring main, another British invention used through out the world
 
just a question regarding lennys job, am i right in saying that you would be allowed to tap off the ring with a single cable to each caravan, rather than the usual two sets of conductors terminated at the equipment/accessory. As lenny has wired his ring main in 25mm2 SWA, then as long as the branch conductor is rated to the same current, or fused down then can you do it. Also if you tapped off at a smaller conductor size, if you then fitted a smaller rated fuse/mcb ect downstream then that would protect the cable. please correct me or confirm my thoughts.

John
 
I don't see any reason why not, as always, it comes down to current carrying capacity and protection, that protection can be upstream OR downstream.
 
Using the rule of thumb factor of 0.67, I could have used 16mm SWA for my ring circuit i.e a 100A OCPD x 0.67 = a CCC of 67A, then you could not do what you suggest.

As I used 25mm though, then yes you could do what you are suggesting as the CCC of the cable exceeds 100A.

As for 'backfusing' it is done, think of tapping off a busbar chamber for instance, it may be a 400A per phase chamber but you could tap off in 16mm singles to a 60A switchfuse as that would be the maximum drawn. I believe there is a maximum distance of chamber to SF though, I'll have to check.
 
Last edited by a moderator:
i was aware of backfusing (never heard it called that though) with regards to switchgear, but was not sure if same principles are applicable to normal installations. Come to think of it, the DNO use backfusing with their supplies, because they are protecting their tap off to your installation, and their ring will be rated to more than 100A
 

Reply to spurs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
731
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
972

Similar threads

Who knows? There's this, in the OSG app H: "Permanently connected equipment should be locally protected by a fuse complying with BS 1362 of...
Replies
3
Views
279
Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
412

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top