- Joined
- May 7, 2012
- Messages
- 117
- Reaction score
- 24
Recently had my inaugural NICEIC Domestic Installer Assessment. My assessor pointed out to me that my Schedule of Inspections was slightly inaccurate in that I had marked "double insulation" as "N/A". He pointed out to me that standard ceiling pendants had no CPC and as such were class 2, double insulated items. Meaning that I should have ticked the "Double Insulation Box". I didn't find myself in a postion to argue with him; indeed his reasoning appeared quite logical. But I recall from the old certificates (not the latest ones) that there used to be a note that stated that Double Insulation was not a suitable method of protection in a domestic installation. Any thoughts from you wise people would be appreciated; just for interest, I have no desire to go head to head with anyone over this matter.