Just been to look at a single static caravan on a farm, they are looking for a EICR to be done.
Incoming supply is TNCS.
80amp DP protected 10mm 2core SWA running 100 meters or more to a outdoor box under caravan containing a 100ma rcd and 16amp mcb, where it has been TTd fine. From this runs a 6mm t+e, clipped direct, feeding a 30ma protected board in the caravan.
Have a couple of things I am unsure about
Is the TTd 6mm t+e submain clipped direct, under the caravan ok protected by a 100ma rcd?
The 100 meters or more 10mm SWA with the volt drop would only be able supply about 10amps to the caravan. Would a 10amp HRC fuse at the incomer and a 10amp 60898 at the caravan provide discrimination of a sort? If not think the caravan will only be able to have a 6amp supply!
Thanks