I've picked up some work doing maintenance on a caravan site. The caravan's are what I would class as static but are all fed via a small 30ma RCD protected enclosure onto a 16a single phase BS4343 socket which has to be 30ma protected because its less than 20A.

The supply is for 5 caravan on a 25mm 2 core radial protected by a 100ma RCD.

The supply is therefore not going straight into the caravan and would then be classed as temporary and fall under section 721 of BS7671, which means that it can't be therefore be supplied via a TNCS supply which it is at the momment. The cpc must be split at the socket and the caravan made a TT system via its own earthing system.

Should it be classed as a static or caravan on the strength that its on a BS4343 socket and fall under section 721 or would you still class it as a static caravan and stay under Bs7671 as a whole.

Any comments will be useful.
 
One of the reasons Caravans are not allowed to be TN-C-S as I understand it, is due to the fact that there is no guarantee the internal wiring of the caravan is up to scratch.
I think that I would go for TT, unless there's some paperwork stating the internal wiring of each of the caravans are up to scratch.
 
I've picked up some work doing maintenance on a caravan site. The caravan's are what I would class as static but are all fed via a small 30ma RCD protected enclosure onto a 16a single phase BS4343 socket which has to be 30ma protected because its less than 20A.

The supply is for 5 caravan on a 25mm 2 core radial protected by a 100ma RCD.

The supply is therefore not going straight into the caravan and would then be classed as temporary and fall under section 721 of BS7671, which means that it can't be therefore be supplied via a TNCS supply which it is at the momment. The cpc must be split at the socket and the caravan made a TT system via its own earthing system.

Should it be classed as a static or caravan on the strength that its on a BS4343 socket and fall under section 721 or would you still class it as a static caravan and stay under Bs7671 as a whole.

Any comments will be useful.

It doesn't matter whether ''static'' or not, PME (TNC-S) cannot supply caravan type installations. This rule applies to both types of park sites, including permanent residential sites. All supplies must be via TN-S or TT.


I take it that main 100mA RCD supplying the 25mm sub-main cable is an S type RCD, ...right??
 
I work at a caravan park with 25mm 2 core feeding exactly the same boxes (rolec) due to the many inherent glanding problems with earth continuity we found it easier to earth spike at regular intervals then even poor glanding continuity doesn't mean loss of earth and even though the earth loop spec for a 30mA rcd is under 1663 ohms it is rare on large installations not to have several failed RCDs even when regularly tested so as low as possible earth loop keeps it safe (Touch Voltage).
 
I work at a caravan park with 25mm 2 core feeding exactly the same boxes (rolec) due to the many inherent glanding problems with earth continuity we found it easier to earth spike at regular intervals then even poor glanding continuity doesn't mean loss of earth and even though the earth loop spec for a 30mA rcd is under 1663 ohms it is rare on large installations not to have several failed RCDs even when regularly tested so as low as possible earth loop keeps it safe (Touch Voltage).

Agree completly with installing a spike at regular intervals.... Shows you know something about TT installations... lol!!!

And as for the observation on RCDs ....I've been saying this for ages here, but the die hard's will not accept the level of RCD failures is High!!!
 
The RCD covering the radials to the caravans is a 's' type RCD its a merlin gerin with integral isolation, and I have completed the work as Section 721 taking a earth rod directly to plug earth feeding the caravan with loop tested out at 56.6 ohm which being <200 ohms according to Table 41.5 note 2 is an acceptable reading. It's just strange to me that 40 caravan on the site where obviously not installed correctly from the out set the client is now asking why i'm the only electrician in 10 years to point out its wrong.

Cheers for your help guys any further comments.
 
im a big beliver in every hook up has its own earth rod just my preferance realy and im always wary of RCD's as engineer 54 has said RCD's do fail and even more when subjuct to damp and some times humid conditions like in ip rated enclosure it only takes a heavy rain shower followed by the sun to cause condense on an RCD that in an enclouser see it all the time here .. may be its because i live in wales when it rains it rains
 
Cant fault the more the merrier on the earth rods, although max impedance is 1667, I have come across numerous problems with RCD's NOT tripping on 5X when the Ze has been high (>100). This has normally highlighted a glanding deterioration at the box. Didnt help on the last one, the wrong fittings had been used, plus the close proximity to the sea (150m)
 
Agreed mate do like it to be less than 200 for stability in fact im fussy i like it to be less than 100 and the salt air plays merry hell with conductors infact any metal fittings too ,as you'll know living in the same area graeme
 
I've picked up some work doing maintenance on a caravan site. The caravan's are what I would class as static but are all fed via a small 30ma RCD protected enclosure onto a 16a single phase BS4343 socket which has to be 30ma protected because its less than 20A.

The supply is for 5 caravan on a 25mm 2 core radial protected by a 100ma RCD.

The supply is therefore not going straight into the caravan and would then be classed as temporary and fall under section 721 of BS7671, which means that it can't be therefore be supplied via a TNCS supply which it is at the momment. The cpc must be split at the socket and the caravan made a TT system via its own earthing system.

Should it be classed as a static or caravan on the strength that its on a BS4343 socket and fall under section 721 or would you still class it as a static caravan and stay under Bs7671 as a whole.

Any comments will be useful.
Hi Strickers,
BS7671, Section 708 applies to Electrical Installations in Caravan / Camping Parks and Similar Locations.
ESQCR 2002, 9(4), prohibits the use of a TN-C-S supply system to a caravan or similar construction (see 708.553.1.14).
708.530.3 States NOTE: Not more than four socket-outlets should be grouped in one location ...
708.533.1.12 States Each socket-outlet shall be provided with individual overcurrent protection.
708.553.1.13 States Each socket-outlet shall be protected individually by an RCD having Characteristics specified in Regulation 415.1.1 The device shall disconnect all live conductors including neutral.
708.533.1.14 States ... For a TN-C-S system, for a supply with a PEN conductor the protective conductor of each socket-outlet shall be connected to an earth electrode and shall comply with the requirements for Regulation 411.5 for a TT system.
 
Last edited by a moderator:
This is an excerpt from BS7430 the Earthing Code of Practice:
21.10 Mobile (touring) caravans and caravan parks
The electrical protection of persons and livestock using, or in contact with, a caravan has to be reliable since a fault to earth
of equipment within that caravan can result in its frame rising to a dangerous voltage above that of the ground on which it is sited.
Any person then touching any metalwork of the caravan while standing outside is open to the risk of electric shock.
Because of the special hazards associated with caravans, the current Electricity Supply Regulations do not permit the use of PME systems for their supply.
Permanent buildings on a caravan park may be treated as if they are ordinary premises and may be supplied and protected by generally adopted methods.
In such cases the main earthing terminal of an installation which is part of a TN-C-S system may be used.

NOTE Residential caravans which are not normally intended to be moved from a caravan park are regarded as permanent buildings.
 
you can never have too much earthing on a caravan park its still far safer to bond the frame to earth and spike it. At least you are relying on a good earth path not some cheap rcd that may or may not fail within 10 minutes of you pressing the test button.
 

Reply to Static or not in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
744
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top