Ok, so you have an old non RCD protected domestic installation on a TT earthing arrangement.
Would it be preferable to upgrade to PME if available by the DNO or stick to TT and protect with up front 100mA RCD if the Ze was ok via the rod?
 
Also with rumours just before the 18th coming out of a move back to requiring earth rods. Was that a sniff of the big boys in the private sector wanting to avoid responsibility for providing an adequate route to earth? :cool:
 
Also with rumours just before the 18th coming out of a move back to requiring earth rods. Was that a sniff of the big boys in the private sector wanting to avoid responsibility for providing an adequate route to earth? :cool:
I think you have a point. The issue with PME is the open circuit PEN conductor - hence the requirement for a rod for PV, outbuilding, shed. So if someone gets fried it’s our responsibility not the DNO, why? Smart meters can shed the load by switching off the supply (volatile renewables?) like I said, it’s all changing. I like TT, you know where you are. My only gripe is the need for a type 1 SPD which are not cheap.
 
When I can, I change TT CU’s to RCBO’s. I don’t really like one central RCD that trips the entire installation. I don’t really get how the overhead TT line could be changed to PME, certainly not in my location.

What's not to get? A lot of overhead lines installed since the 70's will be PME supplies. I don't know if this is universal but in the SSE area every pole that has an earth electrode and N-E link has a label on it with the letters PME in red on a white background. So the availability of PME is easy to check.

One very well respected former member of the forum insisted that only overhead supplies can be true PME supplies.
 
Ok, so you have an old non RCD protected domestic installation on a TT earthing arrangement.
Would it be preferable to upgrade to PME if available by the DNO or stick to TT and protect with up front 100mA RCD if the Ze was ok via the rod?

In this area a lot of overhead PME supplies have a label on the poles where the N-E link have been made, usually red letters on a white background about halfway up the pole. It's an easy way to check the availability of PME
 
SSE have changed a couple for me both on overhead supplies. All they appear to do is check the available Ze. That’s why I asked the original question really as my DNO SSE appear to be quite happy to swap to PME.

All they do on site is check the Ze, someone in the office will already have checked if the overhead lines in the area have been fitted with the required N-E links etc for PME.
 
What's not to get? A lot of overhead lines installed since the 70's will be PME supplies. I don't know if this is universal but in the SSE area every pole that has an earth electrode and N-E link has a label on it with the letters PME in red on a white background. So the availability of PME is easy to check.

One very well respected former member of the forum insisted that only overhead supplies can be true PME supplies.
Fantastic answer! Thanks @davesparks - I’m going to be looking at this moving forward. What I didn’t get was how WE can change the installation to PME, surely that needs to go through the DNO.
 
SP will convert to pme if available. last one i had them to they came same day. no charge. they connected N-E in the head and fitted a 16mm tail from there into a henley.
 
Fantastic answer! Thanks @davesparks - I’m going to be looking at this moving forward. What I didn’t get was how WE can change the installation to PME, surely that needs to go through the DNO.

Yes the DNO need to make the final connection to the head, what we do is prepare the installation to be connected to PME by ensuring the earthing conductor and any bonding are the required size and anything else that needs to be done.
 
I had this argument with the NWEB years ago (long before most of you were born). A TT supply the lecky board wanted to make PME, no bloody way! My reasoning, they were wanting to use my “earth nest” for free. It was far better than their puny rod.

UKPN tried the same trick years later on an 11kV system. The earth nest was 100’s of cast iron piles driven eight foot in to the ground. Somewhere in the order of ½ a mile feet squared in area.

Hi Tony.
 
I think you have a point. The issue with PME is the open circuit PEN conductor - hence the requirement for a rod for PV, outbuilding, shed. So if someone gets fried it’s our responsibility not the DNO, why? Smart meters can shed the load by switching off the supply (volatile renewables?) like I said, it’s all changing. I like TT, you know where you are. My only gripe is the need for a type 1 SPD which are not cheap.

A Type 1 with a minimum rating of 12.5kA too.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

FatAlan

Trainee
Supporter
-
Joined
Location
Surrey
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Stick to TT or go PME?
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28
Unsolved
--

Advert

Thread statistics

Created
FatAlan,
Last reply from
Nigel,
Replies
28
Views
4,108

Advert

Back
Top