You could put a stop & start remote if you comply with the relevant requirements, you would need as a minimum a compliant e-stop adjacent to the compressor to remain, also you would need a means of emergency isolation of the electrical energy which was lockable to comply with PUWER98 adjacent to the compressor.
You will need to check that as you are modifying the controls of a machine that it remains compliant with PUWER98 & if the starter is built into the compressor, then you must review the status of the CE marking if you propose a modification as modifying a CE marked machine invalidates the existing CE marking which then means the machine will no longer comply with PUWER98 regulations.
You should really re CE the machine after the mod, not easy as you are not the maker.

There are 2 things you can do really do the job as you see best and take the risk on any issues that may arise, or walk away, I know what I do!

You should do the mod to meet the requirements of the relevant legislation and referenced standards though.
Thank you for you reply. I take onboard the points you have raised. The switch isolator is situated immediately in front of the compressor controls and has the facility to be locked off. I will discuss the points you have raised in your post with the client and see where we go from there. Thanks for your kind guidance.
Regards Mike.
 
Last edited by a moderator:
agreed with netblindpaul, it is certainly do-able and the safety surrounding the issue is largely down to sufficient safe working proceedures such as "lock tag verify". i feel you can perform what is asked by the customer and its then the customers job to ensure the required safety measures are met
 
A slight left field post here, but what about fitting a timer circuit to automatically shut it down at the end of the college day?
It would be a lot less work than the remote switch.


An even easier approach would be a big neon sign at the exit of the garage saying "turn of the f""£$^"£$^ compressor".
 

Reply to Stop button for a compressor, remote. in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
564
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
760
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

Google tells me that a retic controller is for controlling irrigation systems. I would expect these to have an internal switch, probably volt...
Replies
1
Views
272
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top