Jimmyb

Im I missing something ?

been checking 2 x ring finals yesterday and found the following results :-


R1 Rn R2 R1+R2

0.36 0.36 0.45 0.18 for length of est circuit r1&rn values seem about right

0.47 0.47 1.38 0.35 cant check length with this but most be loose cpc somewhere

I thought well ill check for loose connection on both and found nothing, well I checked all accessible one/what I could find

anyone else got thoughts on this please there is only loose damaged connection
 
You're 95% correct. I always have an issue with the term loose connection. It's poor connection to me.

It doesn't necessarily mean theres a 'loose connection' anywhere - as you've pointed out you can't find it. You could literally open every single socket and find everything tight.

It could mean that the insulation of the cable is nicked instead of the copper at one of the connections somewhere on the ring.

It could also mean theres a socket that you haven't found that has a 'loose connection' or even a damaged cable end thats just about hanging on in there at the terminal.

But yes you're correct, it's a 'loose connection' as you put it somewhere.
 

Reply to Strange loop values in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top