Guest569

80amp main switch RCD, occasionally trips when a couple of circuits are switched on (doesn't matter which circuits) with nothing plugged in.

IR tests all good. Replaced RCD for new. Happens in all weather ( don't think its external )

Only sockets on this consumer unit.

Ive had my guys out at it twice with no joy. New build wiring from 16th edition.

Im going to investigate myself this week, Im sure Ive had loose connections causing tripping before, it about all I can think of, a loose tail somewhere around the main switch.


Anything else to look out for ?

Im pretty certain its not a dodgy nail at floorboard etc its fairly new property and in good condition with chipboard throughout.
 
80amp main switch RCD, occasionally trips when a couple of circuits are switched on (doesn't matter which circuits) with nothing plugged in.

IR tests all good. Replaced RCD for new. Happens in all weather ( don't think its external )

Only sockets on this consumer unit.

Ive had my guys out at it twice with no joy. New build wiring from 16th edition.

Im going to investigate myself this week, Im sure Ive had loose connections causing tripping before, it about all I can think of, a loose tail somewhere around the main switch.


Anything else to look out for ?

Im pretty certain its not a dodgy nail at floorboard etc its fairly new property and in good condition with chipboard throughout.

Ok lets have it right here.
You sent the BOYS out to look at this job twice now to look at why an rcd is tripping and they have not found the fault, how many boys does it take to look at why a rcd is tripping and some basic fault finding??
You then { presumably the boss} turn up for a third visit to the customer with no test gear and guess at it being an outside socket which it turns out it wasnt??
And the customer is happy for you to go back for a fourth time to have another go at it or are you sending the BOYS again??
What im getting at is i would be bloody embarassed to keep showing my face to these people who have the fault and quite surprised they aint got a sparks in to find the fault once and for all.
Poor sods power keeps tripping still after 3 visits by numerous so called sparkies!!
Perhaps you need to employ some new BOYS mate
 
Last edited by a moderator:
Ok lets have it right here.
You sent the BOYS out to look at this job twice now to look at why an rcd is tripping and they have not found the fault, how many boys does it take to look at why a rcd is tripping and some some basic fault finding??
You then { presumably the boss} turn up for a third visit to the customer with no test gear and guess at it being an outside socket which it turns out it wasnt??
And the customer is happy for you to go back for a fourth time to have another go at it or are you sending the BOYS again??
What im getting at is i would be bloody embarassed to keep showing my face to these people who have the fault and quite surprised they aint got a sparks in to find the fault once and for all.
Poor sods power keeps tripping still after 3 visits by numerous so called sparkies!!
Perhaps you need to employ some new BOYS mate


I don't need your opinion on my customer relations thanks pal.

Im not sure how much experience you have in the trade but...you should know faults aren't always clear cut and your certainly in no position to determine how easy this "should" be to solve from the other end of the country.

This one would leave plenty folk scratching their heads I think....Tripping under No load, new RCD, no loose connections, almost new cables throughout, IR good at 250v, no set circuit tripping, various circuits tripping it every few days for no reason. Holds with 3/4 circuits on. Sometimes holds with all circuits on for days.

The guy hasn't moved into the property yet. Its empty. Its also got 6 showers, around 10 bedrooms , 3 lounges, 2 dining rooms, 2 kitchens etc etc ...and around 25 circuits in total. We have done some work in the house but fault was happening before we started.


Hardly "basic fault finding"...so please stop with assumptions


Should also add the boys have been reluctant to take any risks on the job at 1000v or ripping walls etc and quite rightly so ...its a very expensive property.


Got to love this forum.......half the folk who comment would be lost on site but behind the computer - experts !
 
Last edited by a moderator:
an earth leakage meter and a ramp test would be my option. ramp it with no circiuts. then 1 circuit, then 2 until the tripping mA drops. that might lead to the faulty circuit.
 
No its GE , are you thinking about the boards that got recalled ?

Could get earth leakage meter tomorrow...

No I had a spate of Crabtree RCD's fail a couple of years back.

Have you even tried timing it?

You need to ramp it, and if it ramps out around 27 it's all good!

El clamp round the tails and check 1 circuit at a time with the rest turned off
 
an earth leakage meter and a ramp test would be my option. ramp it with no circiuts. then 1 circuit, then 2 until the tripping mA drops. that might lead to the faulty circuit.

Yeah but fault seems to be intermittent which complicates things further....It SHOULD show at 1000V IR if the fault is always there right ?
 
i'd be careful with a 1000V test. always the possibility of something left connected that you may not have seen, like aerial amp in loft.

just a thought..... if, as you say, the property is empty, is there a possibility of damp?
 

Reply to Strange RCD Fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
385
  • Question
I misread it.
    • Like
Replies
13
Views
927

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top