Guest569

80amp main switch RCD, occasionally trips when a couple of circuits are switched on (doesn't matter which circuits) with nothing plugged in.

IR tests all good. Replaced RCD for new. Happens in all weather ( don't think its external )

Only sockets on this consumer unit.

Ive had my guys out at it twice with no joy. New build wiring from 16th edition.

Im going to investigate myself this week, Im sure Ive had loose connections causing tripping before, it about all I can think of, a loose tail somewhere around the main switch.


Anything else to look out for ?

Im pretty certain its not a dodgy nail at floorboard etc its fairly new property and in good condition with chipboard throughout.
 
Simple fault....lol. Plenty would be scratching there head at this one.

Just to clarify...I had a spark and a labourer at the job for 3 hours. I popped in for 1 hour with no test gear to check the obvious....I go back friday and armed with the correct gear I WILL find it..

This is all assuming my guys have done the procedures as they should have ....kinda hoping they have not

The customer has complete trust in me, so please concentrate on your own customer relations !
 
So...The wet leaf thing ....Would any procedures by the experts show this ?


Exactly. Far to many variables to solve over the internet....

I appreciate the advice but don't appreciate posts that assume I know nothing !

Typical of this forum though.
 
Jesus this forum is a joke.

Im more than experienced in domestic fault finding than most on here. Dealing with "council spec" rewires for over 10 years Ive seen it all.


If anyones actually cares to read my initial posts, we have been through the basic procedures and this is not a simple fault. Its guaranteed something bizarre....

Perhaps wind blowing a wet leafy tree on to a dodgy connection somewhere outside ? Just one example that could not be found by any procedure listed so far by the experts ...

Bizarre faults do happen, and I'm certain this one is a strange one ...hence title.

This forum is pretty pathetic, everyone far to quick to assume the OP hasn't got a clue !

You seem to have seen it all and know it all - so go fix it then. Daz

- - - Updated - - -

So...The wet leaf thing ....Would any procedures by the experts show this ?


Exactly. Far to many variables to solve over the internet....

I appreciate the advice but don't appreciate posts that assume I know nothing !

Typical of this forum though.

You keep moaning about this forum, but you keep coming back. Daz
 

Reply to Strange RCD Fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
840

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
385
  • Question
I misread it.
    • Like
Replies
13
Views
927

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top