Joined
Jul 9, 2011
Messages
151
Reaction score
12
Location
Cardiff, but work SW
I'm going round in circles with this fault. We have 12 street lighting lamp posts at our factory, 150W son lamps in each. They were on a 20A MCB and yesterday started tripping. They are basically wired from a 20A MCB (2.5mm), through a relay, out of the relay in 6mm armoured and then outside, where somewhere along the line they are jointed to MICC cables before going to the lamp posts . With me so far? One out of monkeys decided to simply upgrade the MCB to a 32A, which actually held in, even though the cable and MCB for red hot. Obviously this isn't the answer so I've put the 20A MCB back in temporarily. Now, my first guess was that there was a loose connection somewhere which was causing the MCB to get hot, but my understanding is that resistance causes a voltage drop and when I checked the voltage at the posts, it's still hovering around 240 (granted it could have been higher before the fault occurred). Secondly, I've just put the clamp on and it's pulling around 36A, circuit SHOULD be around 7.5A (12 X 150W). But again I've always been under the impression that a high resistance creates heat because there's a large voltage drop across it and the current would more than likely decrease in fact. Anyway, I'm at the end of my tether with this one. Any help would be much appreciated.
Any HELP would be. Could the usual patronisers please not comment, I'm looking for advice NOT a Lecture! :D
 
That L-N reading might not be the lamps ,remove fuses from cut-outs switch on if it does,nt trip mcb refit fuse one at a time till it trips . Is 50 megs on an old micc a bad reading?

I admire your benevolence but I’m pretty sure the BANG test is not a recognised or ever recommended method of fault finding in the regs book. Current and all previous editions included. Although, if you can find it in there, let us know because that information will be like gold dust.:smile:
 

Reply to Street lighting fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top