OP
Hi in the shed I screwed the swa gland into a plastic through box and connected the plastic through box to the bottom of the metal consumer unit in the shed that was so as not to incorporate the house earth
phil
phil
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss stroma assessment this week in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net
Am i seeing something i shouldn't heremmm ok
in the house consumer unit I have fitted a 20RCBO to the swa cable the swa cable runs to the shed into a metal garage consumer unit in the consumer unit there is a 40RCD main switch then a 6 amp mcb and a 16a RCD then I try to test the RCD main switch for the tripping time for the inst cert the house rcbo trip
I hope someone can help out as I have my CP assessment at 10 tomorrow
thanks
Don't think the 16A is an rcd, but yes.Am i seeing something i shouldn't here
House = 20 amp RCBO
Shed 4oamp RCD main Switch
Shed 16 Amp RCD (assume for socket radial?)
Again assuming all are 30mA
so RCBO ----->RCD ---->RCD
Sounds like rock, paper and scissors which one goes first along the line?
Do away with rcbo change for mcb and your garage lights and sockets will be in its own rcdHi in the shed I screwed the swa gland into a plastic through box and connected the plastic through box to the bottom of the metal consumer unit in the shed that was so as not to incorporate the house earth
phil
And hope they don't pick up on division of circuits at the garage boardDo away with rcbo change for mcb and your garage lights and sockets will be in its own rcd
Depends if the assessor is a grumpy gitAnd hope they don't pick up on division of circuits at the garage board
Hahaha... A mate and fellow electrician had his annual AC assessment from NICEIC last month and his assessor told / mentioned to him that quote' it is the new expectation on new installations now, that to avoid unsafe situations in the event of a circuit failing that lighting should be divided between sides of the property rather than floors, so the owner still has lights on each floor in a fault situation'And hope they don't pick up on division of circuits at the garage board
But have you listened to what people have been saying about the rcbo in the house CU? remove that and swap for a MCB. First thing tomorrow or even tonight if you have a store open by you is go get a correct size MCB.hi I have connected the armour into the house earth to cove the swa cable to the shed then in in the shed I connected the gland of the swa cable into the bottom of a plastic through box then connected the plastic through box to separate the earthing types
phil
Hope the niceic assessor showed your mate were it states you have to do this?Hahaha... A mate and fellow electrician had his annual AC assessment from NICEIC last month and his assessor told / mentioned to him that quote' it is the new expectation on new installations now, that to avoid unsafe situations in the event of a circuit failing that lighting should be divided between sides of the property rather than floors, so the owner still has lights on each floor in a fault situation'
so you can have front and back, or left and right but no more upstairs lights downstairs lights on their own circuit.... it might cause poor mrs smith to fall over in the dark i guess. personally i think its a bloody silly idea and i would have told the assessor, no problem, ill put every bloody bulb on its own mcb to keep you happy. if it isn't broke why fix it...
Well I hate to tell you yes he is I will be telling him what I think tomorrow afternoon the sod what size mcb do you think I should replace the rcdo with the cable is 4mm 2 core swa
phil