I put the 20A as the max demand in the shed was only 11.25A so I thought that 20A would be adequate with a 6A for the light and 16A for the socket
phil
phil
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss stroma assessment this week in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net
I agree, hate to be harsh but your assessor tomorrow is going to ask these questions of yourself, so go back to your design calcs and look at the load and any diversity calcs etc then decide on what you think you need.You have designed and installed it so you should know how to size the MCB through calculation.
Is it surface fixed, buried in the ground?Well I hate to tell you yes he is I will be telling him what I think tomorrow afternoon the sod what size mcb do you think I should replace the rcdo with the cable is 4mm 2 core swa
phil
Phil, I think that you are misunderstanding something. The 40A marking on a 30mA RCD does NOT relate to a tripping current. The 40A relates to the amount of current that the switch contacts in the RCD can handle. The RCD does not have any over current protection.#
buried its the 20A rcd to feed in the house to the 40A main switch in the shed cant see any diff to a 60A dno fuse and 100A main switch
As it's 4mm supplying the garage he's got no chance of achieving any discrimination with an appropriate OCPD (mcb type anyway)and probably won't achieve it with the 6amp mcb eitherPhil, I think that you are misunderstanding something. The 40A marking on a 30mA RCD does NOT relate to a tripping current. The 40A relates to the amount of current that the switch contacts in the RCD can handle. The RCD does not have any over current protection.
In the same way, a 100A main switch is just a switch that had contacts that can handle currents up to 100A. That device also provides no over current protection.
Quite honestly your design is not good. If you only have a light and a socket in the outbuilding, you don't need a CU out there. Just the RCBO in the house and a simple switched FCU with a 3A fuse in it for the lights.
But you are where you are now. As above, tske that RCBO out at the house end and put in an MCB big enough to provide discrimination with the 16A MCB in the outbuilding. You need to size it correctly for the size of the SWA cable.
I suggest you get some really nice biscuits for the STROMA guy. You are going to need him on your side!
Hopefully he will update us however it went.Anybody know if the OP passed the Stroma Assessment....