house visit today to quote for rewire lights on the basis the lights had no earth , already made my mind up 99.9% that there is a earth before i even step foot in house.
2 sparks before me said , defo needs rewired no earth

walked in light hanging from ceiling not secured i asked whats the prob customer replied no earth cable at lights , so i visualy tested it ;) and seen all done in conduit ,
grabbed megger done Zs would you believe it a efli reading that was within the max allowed in reg book.

2 companys before never tested at all and said rewire needed 100%

guess im to honest :D
 
Lighting circuits were regularly installed back in the 60's with twin and earth with no integral earth, which doesn't present a problem until class 1 fittings are installed.... But as long as no class 1 fittings are installed, then we can only recommend to the customer. The regulations we work by are not retrospective and as such an install that was new in the 60's has to be viewed on the grounds of the regulations that were in place at that time and can not be deemed unsafe with a condition report. As instructed by local NICEIC inspector.
 
What concerns me here is that and I quote Light hanging from celiling - worry that it was left like that.
Second and I take it you did a test at that point and that point only with a visual for the rest of circuit. I ask why was the end of line not found and a earth path proved and tested there?? before a judgement call is made??? as we all know there could be many breaks in the conduit corrosion plastic JB with no earth continuity a lose conduit downstream from where you tested which may result in high reading that do not comply and you may still not have a complete and healty earth path.
Just curious

Just because we have a earth present at a 1 point does not mean we have a earth

More likely, this is an embedded fully screwed conduit system, so no chance of any plastic JB's. lol
Agree in checking all points on this lighting installation, but the chances are, this conduit system will be good for many more years to come...
 
Funny how habit had me write twin and earth better than some peoples habit of constantly informing a customer of an unsafe condition that doesn't really exist. Then to price for a job that doesn't really need doing. Honesty is the best policy tell them it doesn't have an earth, tell them the reasons why we now install circuits with earths, tell them that that as long as there is no class one fittings its OK and if there is they could be removed to class 2 rather than rewire.
 
What concerns me here is that and I quote Light hanging from celiling - worry that it was left like that.
Second and I take it you did a test at that point and that point only with a visual for the rest of circuit. I ask why was the end of line not found and a earth path proved and tested there?? before a judgement call is made??? as we all know there could be many breaks in the conduit corrosion plastic JB with no earth continuity a lose conduit downstream from where you tested which may result in high reading that do not comply and you may still not have a complete and healty earth path.
Just curious

Just because we have a earth present at a 1 point does not mean we have a earth
You have a valid point but on the other hand he may have simply posted an abridged version in the hope of keeping our attention rather than posting I tested at the first light, then another, then another ......then when I found the highest reading of xx I realised this was the last point of utilisation
 
Was referring to the "professionals" that attended before first post who ether didn't understand that the conduit is a perfectly good earth or wanted to scam the customer.
Honesty is the best policy
 
So the metal conduit is being used as the cpc. If metal fittings were used you would put a flying earth lead from conduit box earth terminal to fitting? Just clarifying as the original posts doesn't say if it is metal or plastic light fittings.
 
So the metal conduit is being used as the cpc. If metal fittings were used you would put a flying earth lead from conduit box earth terminal to fitting? Just clarifying as the original posts doesn't say if it is metal or plastic light fittings.
Yes best practise would always have a flying lead, however if I came accross it on an I&T as long as it had good continuity to fittings would just put it as c3.
 
Most likely they don't understand conduit systems and thought it easier just to opt for the rewire option. Just think how many electricians there must be out there now who have passed a short course, but have no experience at all of anything not covered in the classroom.
 

Reply to stupid or cowboys in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
964

Similar threads

Problems can arise when you get on too well then they think he won’t mind me doing a bit.
    • Friendly
    • Like
Replies
8
Views
464
  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top