how do you work out the size of cpc supplying a sub main? and is it the same method for working out the main earthing conductor size?

cheers in advance
 
Last edited:
how do you work out the size of cpc supplying a sub main? and is it the same method for working out the main earthing conductor size?

cheers in advance

All protective conductors inc the earth are worked out the same way - the only exception is main protective bonds. So it is with either table 54.7 or calculated with the adiabatic. Cables with a cpc already incorporated will comply with the adiabatic if they have been selected properly.

main earth should be at least half the size of the main conductors

No, at 16mm or less the main earth should be equal to csa of line conductor (if not calculated) and at 35mm for a line conductor the protective conductor can be 16mm from table 54.7 .
 
543-01-01 says that CSA of every protective conductor other than equipotential bonding conductors shall be

(i) calculated in accordance with 543-01-1 (adiabatic equation: S=sqrt(I²t)/k

or

(ii) selected in accordance with 543-01-04:

54G says that if the phase conductor is less than or equal to 16mm2 then the protective conductor should be the same size as the phase conductor.


 
thanks for the replys, i'll have a go at the adiabatic later ;)

in ref to pg 29 OSG how can the csa (TT system ) be 4mm unprotected? this seems very small or am i reading it wrong?

That is a minimum size, if you used the table 54.7 it would be very much larger. However that would be complete overkill because, as tel said, pefc will be very small. When you put these small fault current values into the adiabatic you will usually get csa for the cpc in the order of <1mm hence the need for minimum sizes :)
 
yeah definatly add FUDGE factor for rainy days as lower risistance = higher fault current

would the cable from the met to the earth electrode be worked out as per table 4.2 (osg pg 29) ?

if so would green and yellow earth cable be classes as "Protected against corrosion" ?
 

Reply to sub main cpc size? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

totally agree
Replies
12
Views
1K
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
797

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top