how do you work out the size of cpc supplying a sub main? and is it the same method for working out the main earthing conductor size?
cheers in advance
cheers in advance
Last edited:
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss sub main cpc size? in the Australia area at ElectriciansForums.net
so a 16mm twin and earth supply to a sub main on a tncs and tns system requires a 16mm cpc but if its on a tt system the cpc would only need to be 4mm if unprotected and not buried?
how do you work out the size of cpc supplying a sub main? and is it the same method for working out the main earthing conductor size?
cheers in advance
main earth should be at least half the size of the main conductors
thanks for the replys, i'll have a go at the adiabatic later
in ref to pg 29 OSG how can the csa (TT system ) be 4mm unprotected? this seems very small or am i reading it wrong?
would the cable from the met to the earth electrode be worked out as per table 4.2 (osg pg 29) ?
if so would green and yellow earth cable be classes as "Protected against corrosion" ?