ferg

-
Arms
Patron
Joined
Apr 26, 2011
Messages
1,828
Reaction score
2,861
Location
N.W.Scotland
I have seen rather frequently SWA sub mains taken from Henleys protected only by DNO fuse and a stand alone RCD.

I have seen it so often now that I am beginning to question my own knowledge.

My understanding is that the sub main should have it's own OCPD depending on the cable it is protecting.

Is there any possible justification or reason that would make this compliant?

The only possible justification I can think of is that if the Zs at the sub board is still low enough to take out the main fuse under short circuit fault conditions, the likely load on the sub board is lower than the CCC of the cable and that the RCD would operate if an earth fault occurred on the cable at a level that would not cause the main fuse to operate.

Have I missed something here or am I right in thinking this set up is non compliant.
 
personally, i'd always fuse a sub main supply according to it's cable, and in any case ensure that the fuse i fitted was < the dno fuse, hopefully enough less to provide discrimination.
 
There is no justification, it does not comply (unless the SWA is less than 3 metres long and being used as tails)
The suppliers do not permit the cutout fuse to be used as the OCPD for any circuit in the installation.

There's not much more to be said about it really.

I think you have highlighted an issue with my terminology there.
Technically speaking it's not a sub main just very long tails protected by a stand alone RCD.
 
I think you have highlighted an issue with my terminology there.
Technically speaking it's not a sub main just very long tails protected by a stand alone RCD.

If its over 3m long it needs to be a distribution circuit (submain) and therefore needs appropriate OCPD/switchgear.

And unless it's a TT system or other special case an SWA protected by RCD would be causinge to question the design of the circuit.
 
Even in a TT system there should be non-DNO OCPD suitable for the cable, etc.

I don't see anything wrong with using the armour to get the TT's earth rod connection from "outside" (i.e. at DNO cut-out location) into the CU location if it was a long and torturous route, but it would be a little bit unusual.
[automerge]1586185346[/automerge]
Also if the CU is a long way from the RCD it is not a very good design from the point of view of end user having to check two very different locations if, say, the lights go out to find what tripped.

As telectrix says, best to put a switch/fuse at the source and, if it is TT, then put the RCD in the CU as main switch so all likely trip resets are in the one location.
 
Last edited:
Even in a TT system there should be non-DNO OCPD suitable for the cable, etc.

I don't see anything wrong with using the armour to get the TT's earth rod connection from "outside" (i.e. at DNO cut-out location) into the CU location if it was a long and torturous route, but it would be a little bit unusual.
[automerge]1586185346[/automerge]
Also if the CU is a long way from the RCD it is not a very good design from the point of view of end user having to check two very different locations if, say, the lights go out to find what tripped.

As telectrix says, best to put a switch/fuse at the source and, if it is TT, then put the RCD in the CU as main switch so all likely trip resets are in the one location.

If the Ra is low enough for the submain to not require RCD protection then that's OK, but in most cases the submain will need RCD protection in a TT system.
 
If the Ra is low enough for the submain to not require RCD protection then that's OK, but in most cases the submain will need RCD protection in a TT system.

Yes, you are right!

Just after posting I thought about it and realised the RCD has to be at the origin of the system, and the SWA sub-main would be part of that system.
[automerge]1586186010[/automerge]
I guess the good design approach would be to make the origin RCD a 100mA or similar delay type and then to RCD/RCBO all circuits at the CU.

At least that way if there is some fault to earth that could trip an RCD you ought to pick it all up at the CU and hopefully never see the main RCD trip (short of a major fault on the SWA, etc).
 
Gotta say I cant recall coming across this ever but would agree that if I did I would see it as non compliant.
I suppose playing devils advocate if the distribution circuit went from the intake to a remote building as a 100a supply it could be argued that it would be fairly pointless having two 100a OCPD's in series about a foot from each other!
 
Could I just ask about potential issues with extending meter tails when moving a CU? Say if the cu was originally 3 metres away from the DNO fuse and has been moved to say 15 metres from the cut out fuse?
 
If playing Devil's advocate I would say unless you have SWA rated for at least 100A then you could never be sure the DNO would not upgrade a cutout and fit 100A.

So I see the issue is more one of having control over the OCPD setup, and not depending on the DNO that (as already pointed out) is not something you should ever be using for your design.
[automerge]1586203893[/automerge]
Could I just ask about potential issues with extending meter tails when moving a CU? Say if the cu was originally 3 metres away from the DNO fuse and has been moved to say 15 metres from the cut out fuse?

The main issue, and the point of the wiring regs on this, is if you have long cables and it is not specifically designed to protect against damage then you don't have an OCPD under your control for those wires. Yes, you could argue that SWA is protected...
 
Hi - my thought (to be corrected :) ) is the DNO cutout fuse is to protect the DNO cable. They have designed it and judged this to be the best place for it to be positioned, considering safety, functionality, cost and access etc.

The use of the DNO cutout fuse for protection of installation tails is mentioned in Reg 433.3.1 (iii) and if they have agreed then it may be compliant. Otherwise Reg 433.2.2 says 3m.
 
Hi - my thought (to be corrected :) ) is the DNO cutout fuse is to protect the DNO cable. They have designed it and judged this to be the best place for it to be positioned, considering safety, functionality, cost and access etc.

The use of the DNO cutout fuse for protection of installation tails is mentioned in Reg 433.3.1 (iii) and if they have agreed then it may be compliant. Otherwise Reg 433.2.2 says 3m.
I don’t believe that regulation 433.2.2 is applicable for the DNO fuse, more regulations 433.3.1 (ii) and 434.4 (iv)
 

Reply to Sub main OCPD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
801
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
833

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
785
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
487

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top