I have seen rather frequently SWA sub mains taken from Henleys protected only by DNO fuse and a stand alone RCD.
I have seen it so often now that I am beginning to question my own knowledge.
My understanding is that the sub main should have it's own OCPD depending on the cable it is protecting.
Is there any possible justification or reason that would make this compliant?
The only possible justification I can think of is that if the Zs at the sub board is still low enough to take out the main fuse under short circuit fault conditions, the likely load on the sub board is lower than the CCC of the cable and that the RCD would operate if an earth fault occurred on the cable at a level that would not cause the main fuse to operate.
Have I missed something here or am I right in thinking this set up is non compliant.
I have seen it so often now that I am beginning to question my own knowledge.
My understanding is that the sub main should have it's own OCPD depending on the cable it is protecting.
Is there any possible justification or reason that would make this compliant?
The only possible justification I can think of is that if the Zs at the sub board is still low enough to take out the main fuse under short circuit fault conditions, the likely load on the sub board is lower than the CCC of the cable and that the RCD would operate if an earth fault occurred on the cable at a level that would not cause the main fuse to operate.
Have I missed something here or am I right in thinking this set up is non compliant.