elbar

I need to install a sub-main supply cable from the house to a shed approx 100M away. The SWA needs to be 25mm csa for volt drop requirements - I intend to install a 100mA RCD and 40A MCB to protect the cable for overload / fault protection using the armouring as a means of earth. Then with the armouring (which will be PME connected) isolated in an insulated adaptable box, the installation within the shed will have an earth rod ( TT) as a means of earthing.
Is this ok or do I need to run a 3 core sub main?
 
I need to install a sub-main supply cable from the house to a shed approx 100M away. The SWA needs to be 25mm csa for volt drop requirements - I intend to install a 100mA RCD and 40A MCB to protect the cable for overload / fault protection Why if it is a TNC-S earthing system

using the armouring as a means of earth. If using a normal 70c cable the SWA should be fine, most likely a XPLE might struggle, I would calc it out to be on the safe side.

Then with the armouring (which will be PME connected) isolated in an insulated adaptable box, the installation within the shed will have an earth rod ( TT) as a means of earthing.Why are you wanting to TT this installation. Is this for cost as you have bonding requirements
Is this ok or do I need to run a 3 core sub main? Depends on above

See post
 
It is my preference to install a 100mA RCD for additional earth leakage protection as the cable will be cleated at low level along a garden wall for 12M. I am aware that I do not need to do this especially as the Zs reading at the shed will be well within the maximum Zs permitted by BS7671.
The reason for wanting to TT the shed installation is cost reduction in using 2 core SWA rather than 3.
 
Well that is fair enough about the RCD, would never decry anyone wanting to give additional protection if that is what they want to do. Can I ask why 100mA one.

You can export the earth via the SWA cable, providing the SWA is capable and you should achieve that on 70c SWA, the XPLE kind is a little close, but you can use the adiabatic to check.
 
It is my preference to install a 100mA RCD for additional earth leakage protection as the cable will be cleated at low level along a garden wall for 12M. I am aware that I do not need to do this especially as the Zs reading at the shed will be well within the maximum Zs permitted by BS7671.
The reason for wanting to TT the shed installation is cost reduction in using 2 core SWA rather than 3.

The only reason to run a 3 core SWA is if you have extraneous metalwork, such as water pipe etc, the 3rd core is then used as a bonding conductor to extend the TNC-S Equipotential zone. Otherwise there isn't any need for that third core. So do you have a water supply at this shed??
 
The only way I can forsee any damage occuring to the SWA cable would be if someone penetrating the armouring with a pick or something similar, so a 100mA RCD would be ok. A time delay 30MA would be better I know.

Thanks malcolmsanford.
 
For a 2 core SWA cable you need a CSA of 36.1 to comply with the steel wire being your CPC. Your XLPE 25mm cable has a CSA of 42. So the use of the armouring complies as a CPC.

If you use a PVC insulated SWA cable the required CSA remains the same at 36.1, but the PVC insulated Cable gives you a CSA of 60. I think Malcolm is a little worried about the length of your run at 100m, and he may have a point. So if you can get hold of PVC insulated SWA cable, so much the better....


 
The only reason to run a 3 core SWA is if you have extraneous metalwork, such as water pipe etc, the 3rd core is then used as a bonding conductor to extend the TNC-S Equipotential zone. Otherwise there isn't any need for that third core. So do you have a water supply at this shed??

Hi Engineer54,

No there is no water supply to the shed, but you have raised an interesting point. The main purpose of this shed is to house a solar PV inverter. The PV array is to be ground mounted just outside the shed, and with the frame work for mounting the panels being all metal it will be extraneous and shall need to be bonded. I think that the sub main cable needs to be a 3 core. Correct?
 
Hi Engineer54,

No there is no water supply to the shed, but you have raised an interesting point. The main purpose of this shed is to house a solar PV inverter. The PV array is to be ground mounted just outside the shed, and with the frame work for mounting the panels being all metal it will be extraneous and shall need to be bonded. I think that the sub main cable needs to be a 3 core. Correct?

If your mounting them on concrete block foundation footings that are partly or fully embedded into the ground, probably!! You would need to test from the MET to the framework and check if the value is 23 Kohms or not. If over the 23k then no need, but you will i think, need to earth the framework, via the CPC.

Having said that, the frame is outside of this shed, so just may need earthing. No time at the moment to check on typical earthing /bonding arrangements for PV systems. So best to ask the solar boys here what earthing/bonding Reg's cover there installations...
 

Reply to Sub - main supply cable - 2 core or 3 core SWA? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
277
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
1K
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
444

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top