I need to install a sub-main supply cable from the house to a shed approx 100M away. The SWA needs to be 25mm csa for volt drop requirements - I intend to install a 100mA RCD and 40A MCB to protect the cable for overload / fault protection using the armouring as a means of earth. Then with the armouring (which will be PME connected) isolated in an insulated adaptable box, the installation within the shed will have an earth rod ( TT) as a means of earthing.
Is this ok or do I need to run a 3 core sub main?