Considering when the thead started the mains will be in and live by now! I would hope.
Pardon my stupidity Tony, how do you see when a thread is started?
New to forum . . . i've just been clicking the "What's New?" tab, is this not the way to navigate the forum?
Just above the name of the poster shows when it was posted.
wouldn't the thread have been better if the "engineer" had not posted an insult? anyhow all done, I'm sure he will try again, bullies do.
All earth links must be properly fitted, cpc's run to earth terminal of every accessory (socket outlets, switch plates, luminaires etc),
Read more: http://www.electriciansforums.net/c...al/62184-sub-main-supply-4.html#ixzz28do7IFAi
I'm sure he will, I don't do any large industrial work as far as I go is working on old farms (where you'd definitely run a cpc) and the small workshop stuff, how ever it's been interesting to sit back and see the opinions from you and en54
Afraid I am going to get a splinter in my backside, because I am sitting on the fence on this issue! Had a very similar discussion only a day or so ago. Bottom line is, yes, it is acceptable to rely on a properly installed and connected steel trunking system for all cpc's of all circuits. All earth links must be properly fitted, cpc's run to earth terminal of every accessory (socket outlets, switch plates, luminaires etc),and it must be tested thoroughly and achieve results that conform to BS 7671:2008 (2011). The cpc's must be terminated onto the trunking and bolted through effectively etc etc. But I am also aware that many installers prefer to instal separate cpc's, for the added security that they feel a separate cpc offers, should, for any reason the containment system fail. There is of course extra cost but that is their choice. In reality it matters not, the requirements of the Regs. are fulfilled and everyone is happy. I have installed in both ways, mainly the latter in recent years as architects/Q.S's etc have specified it, for reasons of their own, hence I feel the custom has become widely adopted (but NOT necessary). And if it means extra cabling and bigger trunking (and conduit) etc, well good luck with the price if you are tendering against someone who is not installing additional cpc's.
Nowthe earth links are another bug bear of mine. I dont understand what their function is. Im talking about when you already have what i would call joiners, which are usually slightly smaller than the trunking, and fit inside. You then bolt though. Tray joiners are either wrap around or sit on the inside of the lip.
My point is, the copper link does not improve the conductivity of the joint. By bolting a joiner through the tray, ladder, trunking ect, you have already given a fantastic path for possible fault currents. I cant see why we are usually made to go and fit earth straps/links across them.
I only use links on fresh air joins, i jumping from one tray run to another.