sub main | on ElectriciansForums
Discuss sub main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
E
ElectricIANJ
Hi guys im doing a job that needs a sub main to a outbuilding was going to use 16swa but not sure what to do at origin with conecting in to a consumer unit size wise any ways round it or will it fitt ok
best way is to split the tails before the house CU with henley blocks, then into a 63A D/P fused isolator, then your SWA tails to the outbuilding. you could use a spare way on the CU with a 63A MCB. depends on whether you are going to exoprt the earth or TT the outbuilding. why 16mm though. big load?
no need to rcd SWA cable. RCD can go in outbuilding. you can export the earth .
Good question Ian. I've asked it before and not had a satisfactory answer.
The term "equipotential zone" does not appear in the definitions in BS7671 (unless I'm blind).
So, what is it and what defines its boundaries?
OP: it's okay to be cautious, but if you're jumping from 10mm to 16mm just on the basis of caution (rather than sound engineering) are you adding unnecessary cost to the installation?
as i understand it. the equipotential zone is the house. if you are exporting thr earth from the house MET to the outbuilding, you are then making the outbuilding a part of the equipotential zone and so, if you have extraneous metal parts in the outhuse, these must be bonded back to the MET.
yes, but you would take the earth back to the house MET, preferably using a core of your SWA .
now thats somyhing ive not come across, what classes as equipotential zone, not sure im understanding what your saying.
It is what it says on the tin really, it is a zone where all the metalwork is of an equal potential, as Tel says in your home by bonding the services to the main MET you have created a equipotential zone where all that metal work is of an equal potential. This is done by the fact that your MET is connected to the mass of earth either by an earth electrode in a TT system or the DNO provided earth, as they both utilise the earth tapping back at the Transformer. So by bonding the pipework to the MET you are making the potential the same.
As a outbuilding is beyond your equipotential zone then if there are services within the outbuilding you have to create a seperate zone as in a TT system, or if your exporting the earth then you extending the house zone and therefore those services will need to be bonded either with a seprate bonding conductor or a combined bonding/cpc conductor back to the MET at the house.
Reply to sub main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
totally agree
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...