Chr!s
-
Good question Ian. I've asked it before and not had a satisfactory answer.
The term "equipotential zone" does not appear in the definitions in BS7671 (unless I'm blind).
So, what is it and what defines its boundaries?
Agreed, its not mentioned as such, GN5 touches on it a little.
The way i look at it is a zone of equal potential under fault condition.The two main paths of current for electric shock are hand to foot and hand to hand.
Take a single room, Extraneous coper pipe, next to an exposed conductive part. Now if theres a fault on the exposed conductive part there will be a difference in potential between the two, so we bond the pipe, this reduces the touch voltage of hand to hand shock.But what if the floor introduces earth potential, then we must consider hand to foot shock.
When creating an equipotential zone we ensure that simultaneously accessible parts are either at the same potential or make them so they dont introduce potential. Most floors in houses dont introduce earth potential, so the risk considered is hand to hand.
Thats not to say some floors dont introduce earth potential, many tiled or concrete floors may.
So if we export the pme to an outbuilding can we create an equipotential zone?
Is the floor at earth potential?
Are there exposed and extraneous parts?
If we have a broken pen current may flow through the exposed and extraneous parts, now if the floor introduces no potential then theres no risk of hand to foot shock, the risk is hand to hand, but if we bond all exposed and extraneous back to the met then we will have similar potential between the two, so reducing the risk of hand to hand shock.
HTH