Good question Ian. I've asked it before and not had a satisfactory answer.
The term "equipotential zone" does not appear in the definitions in BS7671 (unless I'm blind).
So, what is it and what defines its boundaries?


Agreed, its not mentioned as such, GN5 touches on it a little.

The way i look at it is a zone of equal potential under fault condition.The two main paths of current for electric shock are hand to foot and hand to hand.

Take a single room, Extraneous coper pipe, next to an exposed conductive part. Now if theres a fault on the exposed conductive part there will be a difference in potential between the two, so we bond the pipe, this reduces the touch voltage of hand to hand shock.But what if the floor introduces earth potential, then we must consider hand to foot shock.

When creating an equipotential zone we ensure that simultaneously accessible parts are either at the same potential or make them so they dont introduce potential. Most floors in houses dont introduce earth potential, so the risk considered is hand to hand.

Thats not to say some floors dont introduce earth potential, many tiled or concrete floors may.

So if we export the pme to an outbuilding can we create an equipotential zone?

Is the floor at earth potential?

Are there exposed and extraneous parts?

If we have a broken pen current may flow through the exposed and extraneous parts, now if the floor introduces no potential then theres no risk of hand to foot shock, the risk is hand to hand, but if we bond all exposed and extraneous back to the met then we will have similar potential between the two, so reducing the risk of hand to hand shock.


HTH
 
Hi guys im doing a job that needs a sub main to a outbuilding was going to use 16swa but not sure what to do at origin with conecting in to a consumer unit size wise any ways round it or will it fitt ok

You might want to look at the consumer unit size and construction first, is it metal clad or pvc?

Is the 16mm cable size to allow for a large load or volt drop on a long run?

Check the rating of the consumer unit and indeed, the supply itself before adding large loads.
 
no massive load only a bedsit thing 2rings 2 lighting thats about it will go10mm now ive slept on it ,gland off in to a box on outside keep inner sheath on till hit consumer unit i think
 

Reply to sub main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
904
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

totally agree
Replies
12
Views
1K
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
799

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top