I have an older Crouse Hinds board with a 200A service. Due to recent rehab on the house, I found I have the need to install a sub panel. I installed a QO 125A panel, installed the PVC 1.5 inch conduit, and a 100A Siemens breaker in the Crouse Hinds. I then ran the 3 #2 wires to the box, wrappng the neutral wire in white tape, and installed the ground bars in the box, and yes, I know that the ground bar in the sub is not for the neutrals. So far so good. Here is the rub. I’m trying to find a Neutral bar lug for the Crouse Hinds. This bar is the type that has 2 different size holes, one large flanked by two smaller size through the length of the bar. None of the lug kits will fit. The type that has a screw through the bottom that attaches it to the bar has a screw that is too small for the large hole, and too big for the smaller holes. The other lug I tried has legs that are meant to slide into the wire holes then the screw tightens it to the ground bar. This doesn’t work as the holes are offset due to the difference in sizes and the lug plate is straight across,.

I am at the spot of thinking that I am going to have to undue all the neutral/grounds from the existing bar, replace it with a newer bar and a lug. Because I’m not a pro like you’uns, I want to assure you that this work will be done with the main disconnect off, of course. So my questions are twofold. First, do any of you know of a neutral bar lug kit that would fit the older style bar? No one at the various electrical specialty houses seemed to know of one. I am trying to not have to pull all the whites/bares if I can help it. If not, can I use any brand of neutral/ground bar given that Crouse Hinds no longer exists?

Thanks, folks. I apologize for the length of this, but I want to make sure I am being complete when asking for your expertise.
 
I have an older Crouse Hinds board with a 200A service. Due to recent rehab on the house, I found I have the need to install a sub panel. I installed a QO 125A panel, installed the PVC 1.5 inch conduit, and a 100A Siemens breaker in the Crouse Hinds. I then ran the 3 #2 wires to the box, wrappng the neutral wire in white tape, and installed the ground bars in the box, and yes, I know that the ground bar in the sub is not for the neutrals. So far so good. Here is the rub. I’m trying to find a Neutral bar lug for the Crouse Hinds. This bar is the type that has 2 different size holes, one large flanked by two smaller size through the length of the bar. None of the lug kits will fit. The type that has a screw through the bottom that attaches it to the bar has a screw that is too small for the large hole, and too big for the smaller holes. The other lug I tried has legs that are meant to slide into the wire holes then the screw tightens it to the ground bar. This doesn’t work as the holes are offset due to the difference in sizes and the lug plate is straight across,.

I am at the spot of thinking that I am going to have to undue all the neutral/grounds from the existing bar, replace it with a newer bar and a lug. Because I’m not a pro like you’uns, I want to assure you that this work will be done with the main disconnect off, of course. So my questions are twofold. First, do any of you know of a neutral bar lug kit that would fit the older style bar? No one at the various electrical specialty houses seemed to know of one. I am trying to not have to pull all the whites/bares if I can help it. If not, can I use any brand of neutral/ground bar given that Crouse Hinds no longer exists?

Thanks, folks. I apologize for the length of this, but I want to make sure I am being complete when asking for your expertise.
Normally what I do is drill and tap my own holes. You can go to Lowes or Home Depot or your local hardware and purchase self tapping drill bits and you can get a set that has 6/32-8/32-10/32 drill bits. It doesn’t cost much and then you can purchase any ground bar and make it work. I hope this helps.
 

Reply to Sub panel install on older Crouse Hinds Board in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
The lug to use for this purpose is the Square D / Schneider Electric QO/Homeline 100 Amp Auxillary Neutral Lug Kit for Electrical Panel/Load...
Replies
2
Views
766
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top