Hi everyone,

I recently completed a domestic EICR and came across something unusual. There’s a 10mm² twin and earth cable directly connected to the 100A cut-out fuse at the service head. The cable is concealed within the client’s wall and reappears next to the consumer unit, where it connects to a feeding cable that supplies the neighboring property.

After further investigation, I discovered that this cable is supplying power to the off-license shop next door and two flats above it.

Would you classify this as a C2? I’d appreciate your thoughts on this situation.

[ElectriciansForums.net] Subject: EICR Findings - Advice on Coding Required

[ElectriciansForums.net] Subject: EICR Findings - Advice on Coding Required

[ElectriciansForums.net] Subject: EICR Findings - Advice on Coding Required

[ElectriciansForums.net] Subject: EICR Findings - Advice on Coding Required
 
Hi everyone,

I recently completed a domestic EICR and came across something unusual. There’s a 10mm² twin and earth cable directly connected to the 100A cut-out fuse at the service head. The cable is concealed within the client’s wall and reappears next to the consumer unit, where it connects to a feeding cable that supplies the neighboring property.

After further investigation, I discovered that this cable is supplying power to the off-license shop next door and two flats above it.

Would you classify this as a C2? I’d appreciate your thoughts on this situation.

View attachment 118398

View attachment 118399

View attachment 118400

View attachment 118401
You need to contact the client and inform him that it needs to be disconnected.
If you leave it connected, then you are complicit in theft of electricity.
 

Reply to Subject: EICR Findings - Advice on Coding Required in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top