Unbalanced final ring | Page 3 | on ElectriciansForums

Discuss Unbalanced final ring in the UK Electrical Forum area at ElectriciansForums.net

By chance this popped up on youtube earlier, it shows T+E overloaded to destruction. The experiment is a little flawed IMO, because he doesn't really allow enough time for the smaller overloads to reach their peak temperature, but it still may be of interest.

View: https://www.youtube.com/watch?v=IF2UvUZoO2E
 
I have an old Pichill 180A stick arc welder that gets dragged out occasionally for some heavy duty welding. On a few occasions, when it's been out and I've been bored, I've connected the odd metre or two of T&E or singles between its clamps just to see what happens at various currents.
General conclusion is that it'll take considerably more current than you might think before damage occurs.
 
Why not rebalance the ring by extending it in one of the cavities? It's an old ideology but in theory works. Calculate the length to the two sockets feeding kettle and dryer, for example, by splitting the ring. Then calculate the distance from the other side of the split ring socket back to the CU. L1 = 10m and L2 = 15m, add a 5m figure of 8 onto L2 and reconnect the ring. 15m/15m each side of the ring to the heaviest loads

Diversity wipes out the above though. But something like this I would look to do at design stage and make it a none issue
 
Why not rebalance the ring by extending it in one of the cavities? It's an old ideology but in theory works. Calculate the length to the two sockets feeding kettle and dryer, for example, by splitting the ring. Then calculate the distance from the other side of the split ring socket back to the CU. L1 = 10m and L2 = 15m, add a 5m figure of 8 onto L2 and reconnect the ring. 15m/15m each side of the ring to the heaviest loads

Diversity wipes out the above though. But something like this I would look to do at design stage and make it a none issue
Thx, but:
"L1 = 10m and L2 = 15m, add a 5m figure of 8 onto L2 and reconnect the ring. 15m/15m each side of the ring to the heaviest loads"


Did you mean L1 not L2?
 
Thx, but:
"L1 = 10m and L2 = 15m, add a 5m figure of 8 onto L2 and reconnect the ring. 15m/15m each side of the ring to the heaviest loads"


Did you mean L1 not L2?
I think he means Leg 1 and Leg 2.
 

Reply to Unbalanced final ring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
663

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top