Sunbed Supply | on ElectriciansForums

Discuss Sunbed Supply in the UK Electrical Forum area at ElectriciansForums.net

Joined
Aug 20, 2019
Messages
8
Reaction score
1
Location
Isle Of Wight
Upright Sunbed.
63A supply in 16mm SWA
63A type C MCB to deal with initial inrush of current.
100mA RCD was recommended by manufacturer As 30mA Would cause nuisance tripping.

Maximum earth fault loop impedance value for 63A type C MCB is 0.27.
Ze is 0.21

How do I meet this value? Is there anything I could change to install to increase the max EFLI?
Thanks
 
Upright Sunbed.
63A supply in 16mm SWA
63A type C MCB to deal with initial inrush of current.
100mA RCD was recommended by manufacturer As 30mA Would cause nuisance tripping.

Maximum earth fault loop impedance value for 63A type C MCB is 0.27.
Ze is 0.21

How do I meet this value? Is there anything I could change to install to increase the max EFLI?
Thanks
What is the loading of the sunbed in KW? How did you calculate the cable size and the OCPD size?
 
If your 100mA RCD is upstream of the cable you don't need to worry so much about Ze but you should still meet the disconnection time on a L-N short.

What is the supply PSSC and cable length?
[automerge]1589811055[/automerge]
What is the surge like?
BS88 80A fuse is 0.44 ohm, so you could put that after the MCB and before the cable so a short is cleared in under 5s if your R1+R2 is below 0.23 ohm.
[automerge]1589811525[/automerge]
Ugly for sure, knowing the MCB and fuse have overlapping I-t curves, but it might be a way round the problem without looking at some fancy adjustable MCCB that would allow you to balance just the right fault-clearing time and (hopefully) just out of the switch-on surge trip region.
 
Last edited:
What is the loading of the sunbed in KW? How did you calculate the cable size and the OCPD size?

Sorry, have not installed the sunbed yet. Just quoting.
The only specifications I have are from the client, direct from the manufacturer. That included needing a 63A supply, type C MCB and no 30mA RCD . The KW rating was not on the email. I have carried out work at the premises beforehand so have got Ze value of 0.21
[automerge]1589812337[/automerge]
If your 100mA RCD is upstream of the cable you don't need to worry so much about Ze but you should still meet the disconnection time on a L-N short.

What is the supply PSSC and cable length?
[automerge]1589811055[/automerge]
What is the surge like?
BS88 80A fuse is 0.44 ohm, so you could put that after the MCB and before the cable so a short is cleared in under 5s if your R1+R2 is below 0.23 ohm.
[automerge]1589811525[/automerge]
Ugly for sure, knowing the MCB and fuse have overlapping I-t curves, but it might be a way round the problem without looking at some fancy adjustable MCCB that would allow you to balance just the right fault-clearing time and (hopefully) just out of the switch-on surge trip region.


The length of run on the cable is 10 meters above a suspended ceiling .
I haven’t installed it yet, just quoting for supply and came across this issue. Your idea of having the fuse after the MCB may be the answer??
 
Last edited:
Looking at the Prysmian data sheet 16mm has 1.15mOhm/m for conductor and 3.7mOhm/m for the SWA, so R1+R2 about 4.9 mOhm/m and even for your initial case of Ze 0.21 and required Zs of 0.27 your limit is 0.06 Ohms so max length of 12m so just usable!

Using 3 core SWA so you have a 16mm Cu CPC also joined in parallel with the SWA at both ends gives an R1+R2 impedance of less than 2.3m Ohm/m so max length would be 26m which is a bit more reasonable margin.

So probably it is just OK as it stands, especially if you use 3-core.
[automerge]1589813615[/automerge]
Looking at the book again, there is no disconnect time requirement on an overload (just protection against fire/damage obviously) so simply having a 100mA or 300mA instant RCD before the SWA cable would also allow it to be met easily.
 
Last edited:
Looking at the Prysmian data sheet 16mm has 1.15mOhm/m for conductor and 3.7mOhm/m for the SWA, so R1+R2 about 4.9 mOhm/m and even for your initial case of Ze 0.21 and required Zs of 0.27 your limit is 0.06 Ohms so max length of 12m so just usable!

Using 3 core SWA so you have a 16mm Cu CPC also joined in parallel with the SWA at both ends gives an R1+R2 impedance of less than 2.3m Ohm/m so max length would be 26m which is a bit more reasonable margin.

So probably it is just OK as it stands, especially if you use 3-core.
[automerge]1589813615[/automerge]
Looking at the book again, there is no disconnect time requirement on an overload (just protection against fire/damage obviously) so simply having a 100mA or 300mA instant RCD before the SWA cable would also allow it to be met easily.

Perfect. Thanks for your time mate.
 
The figures I had might be DC resistance, so you ought to allow a bit of margin for AC, but hopefully you have some solution(s) to offer the client. Good luck!
 
When I do these the manufacturers always ask for a 100ma RCD. I take this to mean there is considerable normal leakage to earth and run a separate 10mm copper conductor in addition to the copper cpc to each bed.
 
When I do these the manufacturers always ask for a 100ma RCD. I take this to mean there is considerable normal leakage to earth and run a separate 10mm copper conductor in addition to the copper cpc to each bed.
Yes, if nuisance tripping 30mA ones then must be above 10mA. Though if fed with 3-core SWA you have two CPCs already (assuming armour properly terminated in it).

I have never seen one that close so wondering if they have cable gland holes, etc, you could use a SWA gland on?
 
Yes, if nuisance tripping 30mA ones then must be above 10mA. Though if fed with 3-core SWA you have two CPCs already (assuming armour properly terminated in it).

I have never seen one that close so wondering if they have cable gland holes, etc, you could use a SWA gland on?

I was planning on putting up a 63A vertical interlocked switched socket as there has to be a point of isolation locally outside the bed in case someone gets into trouble and sets the alarm off via a button inside the bed.
 

Reply to Sunbed Supply in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...
Replies
11
Views
554

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top