Peter Wrench

Can I ask a question.

We have had a new bathroom fitted and when they fitted it they removed all bonding from the bathroom including the 10mm to the shower.
When I asked about this the said it was not needed as protected by rcd.
 
There's a bit more to it than just fitting an RCD!

It is true that the requirement for supplementary bonding is less now than it was, but you can't just ignore it.
You should be testing all exposed pipework to establish whether bonding is or is not required. If the pipework is already connected to the installation earth (bonded elsewhere) it is ok and if it's resistance to earth is above a certain value it is also ok. Anything else needs bonding.
In all cases an RCD is still required.
 
Sorry no offence intended.
I was just thinking that even if the pipe work did not require bonding at the time a small change like adding a small piece of plastic pipe down the line could change this.
 
Thank you.
I used to work in the industry, completed 1st year and have only just rediscovered my interest.

I would like to get back into it but not keen on paying 5K for a course that offers no experience.
 
Last edited by a moderator:

Reply to Supplementary bomding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
346
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
885
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Surely one of the most important parts of supplementary bonding is to bond the radiator and hot tap/pipe to the cold one. Both the hot tap and...
Replies
32
Views
2K
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top