Hi,

a recent PIR has picked up no RCD protection and no supplemantry bonding to pipe work.

Am i correct in saying if all circuits to bathroom are protected by RCD then supplementary bonding is not required?
 
Hi,

a recent PIR has picked up no RCD protection and no supplemantry bonding to pipe work.

Am i correct in saying if all circuits to bathroom are protected by RCD then supplementary bonding is not required?

Not quite true, it depends what type of installation you are talking about, SB is still required in a lot of cases.

If you are talking about domestic bathrooms, then all of these conditions need to be met to omit SB,

1) the final circuits meet the requirements for ADS
2) all final circuits in the location have additional protection by means of an RCD 30mA
3) all extraneous conductive parts of the location are effectively connected to the protective equipotential bonding (main protective bonds) to the MET
 

Reply to supplementary bonding and rcd protection in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi I need help with understand supplementary bonding. I know RCD is additional protection and in the even of the fault at leakage of 30mA, it...
Replies
0
Views
41
  • Question
Surely one of the most important parts of supplementary bonding is to bond the radiator and hot tap/pipe to the cold one. Both the hot tap and...
Replies
32
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top