where a RCD is fitted, R<= 1667. the 0.05 is considered to be a negligible resistance between different extraneous metal parts and MET. in other words, the OCPD is guaranteed to trip within the required time.
 
Last edited:
I was going to do my continuity tests, and was quite confident that using the formulae from reg. 415.2.2; R< 50/Ia ,where in the case of a 6amp BS EN 60898 MCB Ia = 30amp. Therefore R=50/30 < (less than) 1.666ohms. However, talking to another electrician, he said the reading should be below 0.05ohms. Can anyone advise?
You are correct.
 
I was going to do my continuity tests, and was quite confident that using the formulae from reg. 415.2.2; R< 50/Ia ,where in the case of a 6amp BS EN 60898 MCB Ia = 30amp. Therefore R=50/30 < (less than) 1.666ohms. However, talking to another electrician, he said the reading should be below 0.05ohms. Can anyone advise?

Did my tests. Pipes in heater cupboard, all 0.00-0.05ohms. Same pipes to MET, 0.00-0.05ohms. Extraneous conductive parts in bathroom (i.e. cold & hot supply to basin & rads & connecting pipework) > 99.9kohms. Same result to cpc of circuits in bathroom. On inspection of cupboard under kitchen sink, plastic water main to plastic pipe, to short peice of copper to sink. I suspect the house is plumbed predominantly in plastic pipe, with the last visible peice in copper, which I believe does not require bonding.
 
Pipes in heater cupboard, all 0.00-0.05ohms. Same pipes to MET, 0.00-0.05ohms.
It would seem they are already bonded and satisfactory.
0.05 is just an accepted value of negligible impedance and does not relate to any test as such, other than a satisfactory connection.


Extraneous conductive parts in bathroom (i.e. cold & hot supply to basin & rads & connecting pipework) > 99.9kohms. Same result to cpc of circuits in bathroom.
Then they do not require bonding and should not be bonded.
If that is the maximum range reading it could be a lot higher. You could test with IR.


On inspection of cupboard under kitchen sink, plastic water main to plastic pipe, to short peice of copper to sink. I suspect the house is plumbed predominantly in plastic pipe, with the last visible peice in copper, which I believe does not require bonding.
Correct.
 
Out of interest; I was reading somewhere on this forum that if the R < 1667ohms, the extra' cond' should be bonded R> 22kohms it does not, I know that's noy quite right, but I can't find that thread now. What formulea are used for such figures, and where does that appear in the regs?
 
I believe all would be revealed in GN8 (guidance note 8) - the earthing and bonding one. Pretty sure its in that one. If not then its GN3, the testing and inspection one.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Midwest

Arms
-
Joined
Location
Oxfordshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Retired Electrician

Thread Information

Title
Supplementary Bonding - How was it wired?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
42

Advert

Thread statistics

Created
Midwest,
Last reply from
Richard Burns,
Replies
42
Views
7,935

Advert

Back
Top