where a RCD is fitted, R<= 1667. the 0.05 is considered to be a negligible resistance between different extraneous metal parts and MET. in other words, the OCPD is guaranteed to trip within the required time.
 
Last edited:
I was going to do my continuity tests, and was quite confident that using the formulae from reg. 415.2.2; R< 50/Ia ,where in the case of a 6amp BS EN 60898 MCB Ia = 30amp. Therefore R=50/30 < (less than) 1.666ohms. However, talking to another electrician, he said the reading should be below 0.05ohms. Can anyone advise?
You are correct.
 
I was going to do my continuity tests, and was quite confident that using the formulae from reg. 415.2.2; R< 50/Ia ,where in the case of a 6amp BS EN 60898 MCB Ia = 30amp. Therefore R=50/30 < (less than) 1.666ohms. However, talking to another electrician, he said the reading should be below 0.05ohms. Can anyone advise?

Did my tests. Pipes in heater cupboard, all 0.00-0.05ohms. Same pipes to MET, 0.00-0.05ohms. Extraneous conductive parts in bathroom (i.e. cold & hot supply to basin & rads & connecting pipework) > 99.9kohms. Same result to cpc of circuits in bathroom. On inspection of cupboard under kitchen sink, plastic water main to plastic pipe, to short peice of copper to sink. I suspect the house is plumbed predominantly in plastic pipe, with the last visible peice in copper, which I believe does not require bonding.
 
Pipes in heater cupboard, all 0.00-0.05ohms. Same pipes to MET, 0.00-0.05ohms.
It would seem they are already bonded and satisfactory.
0.05 is just an accepted value of negligible impedance and does not relate to any test as such, other than a satisfactory connection.


Extraneous conductive parts in bathroom (i.e. cold & hot supply to basin & rads & connecting pipework) > 99.9kohms. Same result to cpc of circuits in bathroom.
Then they do not require bonding and should not be bonded.
If that is the maximum range reading it could be a lot higher. You could test with IR.


On inspection of cupboard under kitchen sink, plastic water main to plastic pipe, to short peice of copper to sink. I suspect the house is plumbed predominantly in plastic pipe, with the last visible peice in copper, which I believe does not require bonding.
Correct.
 
Out of interest; I was reading somewhere on this forum that if the R < 1667ohms, the extra' cond' should be bonded R> 22kohms it does not, I know that's noy quite right, but I can't find that thread now. What formulea are used for such figures, and where does that appear in the regs?
 
I believe all would be revealed in GN8 (guidance note 8) - the earthing and bonding one. Pretty sure its in that one. If not then its GN3, the testing and inspection one.
 

Reply to Supplementary Bonding - How was it wired? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
791
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

Hi I need help with understand supplementary bonding. I know RCD is additional protection and in the even of the fault at leakage of 30mA, it...
Replies
0
Views
101
  • Question
The chances of any problem without the RCD are minimal, including it extremely negligible......with the supplementary, on a kin to Hannibal Lector...
Replies
6
Views
846

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top