where a RCD is fitted, R<= 1667. the 0.05 is considered to be a negligible resistance between different extraneous metal parts and MET. in other words, the OCPD is guaranteed to trip within the required time.
I was going to do my continuity tests, and was quite confident that using the formulae from reg. 415.2.2; R< 50/Ia ,where in the case of a 6amp BS EN 60898 MCB Ia = 30amp. Therefore R=50/30 < (less than) 1.666ohms. However, talking to another electrician, he said the reading should be below 0.05ohms. Can anyone advise?
You are correct.
Did my tests. Pipes in heater cupboard, all 0.00-0.05ohms. Same pipes to MET, 0.00-0.05ohms. Extraneous conductive parts in bathroom (i.e. cold & hot supply to basin & rads & connecting pipework) > 99.9kohms. Same result to cpc of circuits in bathroom. On inspection of cupboard under kitchen sink, plastic water main to plastic pipe, to short peice of copper to sink. I suspect the house is plumbed predominantly in plastic pipe, with the last visible peice in copper, which I believe does not require bonding.
It would seem they are already bonded and satisfactory.
0.05 is just an accepted value of negligible impedance and does not relate to any test as such, other than a satisfactory connection.
Then they do not require bonding and should not be bonded.
If that is the maximum range reading it could be a lot higher. You could test with IR.
Correct.
Out of interest; I was reading somewhere on this forum that if the R < 1667ohms, the extra' cond' should be bonded R> 22kohms it does not, I know that's noy quite right, but I can't find that thread now. What formulea are used for such figures, and where does that appear in the regs?
I believe all would be revealed in GN8 (guidance note 8) - the earthing and bonding one. Pretty sure its in that one. If not then its GN3, the testing and inspection one.
Midwest
Oxfordshire
Retired Electrician
Supplementary Bonding - How was it wired?
Midwest,
Richard Burns,
TrueNAS JBOD Storage Server