supplementary bonding resistance | on ElectriciansForums

Discuss supplementary bonding resistance in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

H

havoone

reg 415.2.2, say i have a 20A breaker. is this then 50V/20= 2.5 ohms. and am i right in saying that the actual test of the supplementary bonding conductor is done with a low reading ohmeter and should not exceed 2.5 ohms ? thank you.
 
reg 415.2.2, say i have a 20A breaker. is this then 50V/20= 2.5 ohms. and am i right in saying that the actual test of the supplementary bonding conductor is done with a low reading ohmeter and should not exceed 2.5 ohms ? thank you.


It's not, mate.

If its a type B 60898 then....

It's 50v/100A = 0.5 ohms.......this is the resistance between two simultaneously accessible, exposed/extraneous conductive parts, and would be tested with a low resistance ohm meter.

You don't use the rating of the breaker, you use the current that is required to trip the breaker in 5 sec or less.....which is 100A:)

Is there a reason you're considering this method of additional protection?
 
not considering it. its a question in a 2382 paper, its a type c breaker in the question.but see my mistake now. i now have to look at time current tables in App 3 and its 200A for a type c. so 50V/200=.25 ohms. and the measured resistance should be equal to or less than this. thanks waynel
 
Last edited by a moderator:

Reply to supplementary bonding resistance in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
344
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
882
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
  • Question
Surely one of the most important parts of supplementary bonding is to bond the radiator and hot tap/pipe to the cold one. Both the hot tap and...
Replies
32
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top