Come on chaps is relatively straight forward...
There are two conditions that exist in a location where you are naked and wet and hanging onto two metal bathroom components
1/ they are exposed
2/ they are extraneous
If they are exposed then they will be connected to the MET through the cpcs and 411.3.2.2 applies with 415.1
If they are extraneous then two further conditions are available:
1/ If they are connected to the MET via MPB and all metal pipework then 411.3.1.2 applies
2/ If they are isolated from the MET because of , either non metal pipework then GN5 and GN8 applies, that is
rx<= Uo/0.01 - 1k ohms which equates to 22k Ohms
So as long as simultaneously touchable metalwork is either bonded to MET or 'isolated' then you have some form of protection.
The confusion arises at what point does isolation stop and bonding begin.
Bonding to the MET infers that the touch voltage will not rise above 50V.
example: A lighting circuit protected by a 6A MCB has a maximum Zs of 7.67 Ohms which complies with table 41.3 but when compared with the requirements of 415.2 must not rise beyond 50V, so an alternative Zs tied down to the surrounding metalwork must be 50/Ia which would be 30A for a 6A MCB. This gives us a maximum Zs of 1.67 Ohms.
Now when used in conjunction with a 30mA RCD in compliance with 411.3.1.2, 415.2, 701.415.2
then Zs < Uo/IAN = 230/30mA
= 7.67 k ohms
This appears to comply with the disconnection time of < 40ms
However, even at 40ms (2cycles of ac) may still be sufficient to provide a kill
So to comply with touch voltage we have
Zs < 50/30mA = 1.67 k ohms
This satisfies both compliance for disconnection times 411.3.2.2 and compliance with 411.3.1.2
Now the problem arises when the resistance between simultaneously touchable parts sits somewhere between being bonded (> 1.67 kOhms) and Isolation (< 22k Ohms)
At this level both RCD and supplementary bonding needs to be present... cheaper just to supp. bond everything
Argue amongst yourselves