Yes - so from the red text above I need to add supp bonding if my Zs is exceeding 1.67ohms (no RCD). But if I can't touch anything on the lighting circuit simultaneously with extran parts why use Ia of the lighting circuit. If the earth fault was introduced, lets say by an immersion heater protected by a 40A MCB and no RCD. Ia would then be 200A (from Fig 3A4) and so your calculation would be 50/200 = 0.25ohms. In other words shouldn't we be using the largest value of Ia in the installation rather than the largest value of Ia in the room containing the bath or shower.

Yes I agree, If the lights or shaver sockets in the bathroom are class II or out of simultaneous reach. I was thinking along the lines of a snagged cable loose above the bathroom making fortuitous contact with the plumbing pipes as stuff gets moved about in loft spaces.

I chose a lighting circuit really to demonstrate that an earth fault voltage sitting on extraneous metalwork does not have to be 0.05 ohms, the largest Zs allowable which would keep the touch voltage to a maximum of 50V. If you had a 10.8kW instantaneous water heater which had caused an earth fault right above the cast iron bath you were standing in while having a shower then you would need a theoretical resistance path to the MET and around the bathroom to be no higher than 50/250 = 0.2 ohms. (personally I would prefer in this case the bath to be isolated from the MET and surrounding metalwork)

Now that RCDs exist and a global 0.4s disconnection time on final circuits, the importance of 'front line' protection by the use of supplementary bonding has lost its importance.

But we still have uncontrolled conditions out side of the installation such as network fluctuations in voltages, lost, damaged, or high resistance supply neutrals, which can lead to voltages appearing on simultaneously touchable metalwork for longer periods than 0.04, 0.4s, 5s. Voltages from PME systems could be there indefinitely until someone with wet hands and feet comes into contact.
 
Yes I agree, If the lights or shaver sockets in the bathroom are class II or out of simultaneous reach. I was thinking along the lines of a snagged cable loose above the bathroom making fortuitous contact with the plumbing pipes as stuff gets moved about in loft spaces.

I chose a lighting circuit really to demonstrate that an earth fault voltage sitting on extraneous metalwork does not have to be 0.05 ohms, the largest Zs allowable which would keep the touch voltage to a maximum of 50V. If you had a 10.8kW instantaneous water heater which had caused an earth fault right above the cast iron bath you were standing in while having a shower then you would need a theoretical resistance path to the MET and around the bathroom to be no higher than 50/250 = 0.2 ohms. (personally I would prefer in this case the bath to be isolated from the MET and surrounding metalwork)

Now that RCDs exist and a global 0.4s disconnection time on final circuits, the importance of 'front line' protection by the use of supplementary bonding has lost its importance.

But we still have uncontrolled conditions out side of the installation such as network fluctuations in voltages, lost, damaged, or high resistance supply neutrals, which can lead to voltages appearing on simultaneously touchable metalwork for longer periods than 0.04, 0.4s, 5s. Voltages from PME systems could be there indefinitely until someone with wet hands and feet comes into contact.

Thanks for this reply and your previous one which was most informative. I now have a much better understanding. Maybe I have not articulated myself very well throughout this thread but it is 415.2.2 (using R</ 50 V/Ia to determine the effectiveness of SEB) that is causing me all the confusion. And which value of Ia to use. This and other forums suggest that you should be using the highest value for Ia that exists in the circuits actually in the room containing the bath or shower. I think that you should be using the highest value of Ia in the whole installation. Any thoughts on that interpretation?
 
Thanks for this reply and your previous one which was most informative. I now have a much better understanding. Maybe I have not articulated myself very well throughout this thread but it is 415.2.2 (using R</ 50 V/Ia to determine the effectiveness of SEB) that is causing me all the confusion. And which value of Ia to use. This and other forums suggest that you should be using the highest value for Ia that exists in the circuits actually in the room containing the bath or shower. I think that you should be using the highest value of Ia in the whole installation. Any thoughts on that interpretation?

The value of Ia will depend on the size of protective device used, that's precisely why 0.05 ohms is mentioned in GN3 as a rule of thumb. A coverall situation/application. I only use lighting as an example of one type of a circuit that will be in use while electric immersion,bath/towel/shower/convector/heaters are being removed for other forms of heating and is common to all bathrooms.

My interest is in knowing the limitations. We know the minimum desirable value of supp.bonding (< 0.01 ohm) But do we know what the maximum R would be or to see it the other way around, the minimum IR value to achieve an 'effective' isolation in the case of a fault or wayward external voltages affecting the potential on internal metalwork .
 
Come on chaps is relatively straight forward...

There are two conditions that exist in a location where you are naked and wet and hanging onto two metal bathroom components

1/ they are exposed
2/ they are extraneous

If they are exposed then they will be connected to the MET through the cpcs and 411.3.2.2 applies with 415.1
If they are extraneous then two further conditions are available:

1/ If they are connected to the MET via MPB and all metal pipework then 411.3.1.2 applies
2/ If they are isolated from the MET because of , either non metal pipework then GN5 and GN8 applies, that is

rx<= Uo/0.01 - 1k ohms which equates to 22k Ohms

So as long as simultaneously touchable metalwork is either bonded to MET or 'isolated' then you have some form of protection.

The confusion arises at what point does isolation stop and bonding begin.

Bonding to the MET infers that the touch voltage will not rise above 50V.

example: A lighting circuit protected by a 6A MCB has a maximum Zs of 7.67 Ohms which complies with table 41.3 but when compared with the requirements of 415.2 must not rise beyond 50V, so an alternative Zs tied down to the surrounding metalwork must be 50/Ia which would be 30A for a 6A MCB. This gives us a maximum Zs of 1.67 Ohms.

Now when used in conjunction with a 30mA RCD in compliance with 411.3.1.2, 415.2, 701.415.2

then Zs < Uo/IAN = 230/30mA

= 7.67 k ohms

This appears to comply with the disconnection time of < 40ms

However, even at 40ms (2cycles of ac) may still be sufficient to provide a kill

So to comply with touch voltage we have

Zs < 50/30mA = 1.67 k ohms

This satisfies both compliance for disconnection times 411.3.2.2 and compliance with 411.3.1.2

Now the problem arises when the resistance between simultaneously touchable parts sits somewhere between being bonded (> 1.67 kOhms) and Isolation (< 22k Ohms)

At this level both RCD and supplementary bonding needs to be present... cheaper just to supp. bond everything

Argue amongst yourselves
Looking for some kind of official source for meeting disconnection times/Zs and keeping touch voltage below 50v on both TN systems not just TT -Pre RCD or just without RCD with Fuses and MCB.

Maybe some old BS7671 or old Book, Workshheet etc? not sure I've got anything before 16th but if you point me in the right direction that would be great, Thanks
 
Last edited:
I've seen this and it's good but it does say


"Note that the touch voltage
may rise above 50 v; the
value of 50 v is used as a
constant in the formula to
ensure sufficient current is
flowing to operate the RCD."

so still a bit confused???
is 50v touch voltage really a thing?
 

Reply to Supplementary Equipotential Bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
912

Similar threads

Hi I need help with understand supplementary bonding. I know RCD is additional protection and in the even of the fault at leakage of 30mA, it...
Replies
0
Views
24
  • Question
Thats a freak accident though, it could just as easilly been anything that killed him. It could very well have been a double insulated bench...
    • Like
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top