Suppliers Earth TN-S | Page 2 | on ElectriciansForums

Discuss Suppliers Earth TN-S in the Australia area at ElectriciansForums.net

R

Roger

Is it ok for you to connect to it ? earth clamp to sheath.

I had a call tonight and a customer could not reset his RCD so no power at all.Ok fixed the fault unlpugged the kettle and it reset as soon as we plug it in it tripped so power all restored.Bid disadvantage of having 1 RCD for whole house.
Double checked earth loop and got over 8.2 ohms on 32amp ring main and thought it could be a loose connection so did cooker socket and got 7.92 for a 40 amp MCB.
Nice bit of 10mm cable on gas and water but no EARTH at meter head,no MET nothing.Had board changed about 10 years ago he said.
All the houses roughly the same in the street all built same time so popped next door and they had a TN-S.Soldered to a wide strip of woven braided steel strap.
So fitted a clamp on cable sheath ,16mm to a MET and 16mm to CU and gas and water connected ,rechecked and got 0.62 ohms on ring so happier now.
I am amazed that it had no earth at all and had been like it for years.It has even had a new digital meter fitted and you would have thought that the meter fitter might have noticed.
No cup of coffee as kettle knackered but £10 tip for coming out.
Should i inform DNO ?
 
same problem i've got right now in my own home have just phoned dno and keep getting fobbed of. So from my connection get no reading but have a reading of the sheath, so not a good idea to put my own clamp on?
[ElectriciansForums.net] Suppliers Earth TN-S
 
so i take it you work for a DNO then?

be realistic, weve all used an earth clamp around the sheath at one time or another so we could get our job done..... its not hurting anybody

You take it wrong I do NOT work for a DNO.

IF you are admitting tampering with DNO equipment then I suggest you don't do it in a public forum.
It is a criminal offence.
Oh, and NO we have not ALL done it at some, just because your standards are down in the gutter does not mean mine are.
I am an NICEIC AC amongst other things.

It could hurt someone and it is a criminal offence.

My local DNO used to fit them, now they won't even tough them live, they disconnect and then deal with them if they have to.
IT IS WRONG.
If the DNO has provided TN-S, brush up on your law and get them to maintain it, or get them to come and to an emergency repair, else TT it and job done.

I thought that the members here had greater competence than this, I was oh, so, so, mistaken.

I am appalled that you not only do this but advocate it to others,
 
You take it wrong I do NOT work for a DNO.

IF you are admitting tampering with DNO equipment then I suggest you don't do it in a public forum.
It is a criminal offence.
Oh, and NO we have not ALL done it at some, just because your standards are down in the gutter does not mean mine are.
I am an NICEIC AC amongst other things.

It could hurt someone and it is a criminal offence.

My local DNO used to fit them, now they won't even tough them live, they disconnect and then deal with them if they have to.
IT IS WRONG.
If the DNO has provided TN-S, brush up on your law and get them to maintain it, or get them to come and to an emergency repair, else TT it and job done.

I thought that the members here had greater competence than this, I was oh, so, so, mistaken.

I am appalled that you not only do this but advocate it to others,


better than having no earth though you have to agree.

i know no one will admit to it. i mean even i am just speaking **hypothetically** but you would be amazed at how many people cut tags to pull the main fuse and use bonding clamps on the sheath
 
ok, if it's so wrong, answer me this. then . called DNO in january, told them i was not happy with the earthing on a client's house. a pme earth terminal was fitted to the cut-out but had not been linked to the neutral. basically the only earthing was through the water pipe bonding. i finally got an answer from DNO last week. should i have left the installation in a dangerous condition for 5 months, or fiited a clamp.? i know what i consider the best option.
 
bororobbo,
It should not have been left with no earth, you have a legal option. TT.
However the DNO have a legal duty to maintain their network.
They should respond in a timely manner.
If you cannot solicit this response then you need to research a little and speak to them in terms they will underdstand, take copious notes during the phone call, names and ext. numbers when you report the lethal condition with their equipment so that you can ensure that this information is passed on to the authorities in the event of a fatality.

telectrix,
How did you confirm this without breaking the law?
See my comments above.

Also, breaking seals and removing cut out fuses is also illegal, unless you have written authority from the DNO, appropriate training and appropriate PPE.

Please go and do an FMEA on these and see what you come up with, then you'll understand why this work is controlled.
 
bororobbo,
It should not have been left with no earth, you have a legal option. TT.
However the DNO have a legal duty to maintain their network.
They should respond in a timely manner.
If you cannot solicit this response then you need to research a little and speak to them in terms they will underdstand, take copious notes during the phone call, names and ext. numbers when you report the lethal condition with their equipment so that you can ensure that this information is passed on to the authorities in the event of a fatality.

telectrix,
How did you confirm this without breaking the law?
See my comments above.

Also, breaking seals and removing cut out fuses is also illegal, unless you have written authority from the DNO, appropriate training and appropriate PPE.

Please go and do an FMEA on these and see what you come up with, then you'll understand why this work is controlled.
i confirmed it by measuring Ze, PSSC and PEFC. and as for taking copios notes, etc. etc. i've got a living to earn, not spend time in futile, non-paying, horrendously costly phone calls ( 0845 from mobiles is 35p/min. listening to endless recorded messages and stupid your call will be answered as soon as possible") . i'd rather jump off the mersey ferry.
 
telectrix,
I have had the same on a new install in an unoccupied building.
Had a next working day response from DNO, as it was unoccupied and we had a reasonable earth through the structural steelwork.
If the building had been occupied they would have been there within hours tops as an emergency call out to a dangerous situation, and of their making.
This is what you should have done is get them to provide you with the service they are legally obliged to.
Else TT the install simple.
To leave the install as was without issuing an EDN and shutting the install down is criminally negligent.

It just gets worse!

I can't believe you left a dangerous installation in service for 5 months, or are you saying you broke the law to make it in your opinion safe, in a manner which in the eyes of the ESC, the NIC, probably the IET & the DNO's is dangerous in itself?

Which one of these criminal, incompetent and downright dangerous acts was it?

I don't know whether it is worth staying around here, I don't want to be associated with so called professionals that think such actions acceptable!

This beggars belief and is no better than the DIY'er or other "persons unknown" undertaking other dangerous electrical installation works.

As well as the badge some of you are sporting in your sigs that DIY electrics is dangerous, perhaps you need to think about the fact that electricla contractors undertaking DIY works on the national grid is dangerous and also illegal!

So next time you need a new supply what are you gonna do, dig the road up and run it in yourself, why not, you work on the grid all the time it seems.
 
as regards, " being there within hours". took 3 days to write to me saying they would arrange a visit " within 5 working days". 12 phone calls and 4 months later, had a phone call " can't provide an earth at the location. you'll have to TT it".
now. i'll tell you what i did.
i borrowed a trained meerkat from compare the meerkat.com. sent him with a fine cord up inside the new studded wall into the attic, then out through a rat hole in the gable end, across a tiled roof, down a drainpipe, then used the fine cord to pull a 10mm earth cable to the edge of the cesspit ( nice and damp ) and drove in a 20ft length of galvanised scaffold pole. to this i clamped ( using 5 BS951 clamps ) the 10mm earth, then covered the termination with industrial grade chip fat ( to minimise the effects of corrosion ). and whacked it all down with a 14lb sledge ( santa don't need it for a few months yet ). only got a decent Ze when the meerkat piddled on the chip fat.

needless to say, no meerkats were harmed in the performance of the above excercise.
 
Its a shame that the sentiments displayed in the reply are not evident in the electrical industry in its entirety

I am sure all who work in the industry would be more than happy to see all available codes and practices carried out safely and by competent people
The reality of the industry is that self interested parties throughout,put selfish interest before safety
Thats as much a critisism of the suppliers as any spark playing with equipment that is off limits to them

Electrical installation,the working with that installation, and competency, are mainly not an initial requirement
Its only when things go ---- up that competence plays any part

Un informed members of the public routinely carry out dangerous life threating acts with electrical installation with the blessing of the countrys powers that be,look at the freedom permitted in all legistlation for electrical installation control or lack should I say

Danger is relative,the chances of me getting something wrong playing with the suppliers equipment is almost nil.zero even
The chances of a diyer getting their un trained installation to bite them is much much higher

Its difficult to take issue with any of the hyper dangerous warnings given,because they are real, because of that danger present
In the real world though,electricity has been around a lot longer than the H+S brigade and with no more fatalities before that H+S brigade sprouted wings

Responsibility for your own personal welfare seems to be an horrendous concept to the members of the brigade,yet personal responsibility has had a far higher success in keeping people safe than all the regulation that is sprouted to replace it

A little over sensitive to the "thou shallt not" code I suggest
 
Looks like as usual there’s a big difference between utopia and reality.
Yes we should stick to the letter of the law. The DNO will arrive on their magic carpet within half an hour. Fix the problem with a wave of their magic wand.
Now lets put our realist hat on, the DNO will arrive on an ox cart 3 months after you’ve asked them to attend. Not having the gear needed they’ll clear off for a fortnight.
As a responsible person what do you do for the customer:
· walk away and pretend you’ve not seen the problem
· tell them and put the fear of god up them for the next few months
· do what you can with what you’ve got to hand?
 
Blimey up to 3 pages now,i only asked whether I should inform the DNO.

My own house is TN-S and it has a BS951 clamp fitted and was fitted when we moved in as the service head was loose and they came to fix it as i can not touch that obviously !
My last experience of calling out a DNO took 4 phonecalls and 5 weeks before they came and PME'd it.They did not charge though.
Ok it was not the best thing to do but i had checked that the earth was there,i took all the necessary reading and proved the sheath provided the earth,albeit used the wrong clamp and should not have touched it.

Its all very well quoting the law and having harsh arguments on here and obviously a few members now rubbed up the wrong way but this is good as the object of this forum is to educate and for me to learn what i do not know.
Or have yet to read from one of my many books that i now own.

I do not know it all but lifes an education.

Now where's my blowtorch and solder ! (only joking 'netblindpaul')
 
I'm with netblindpaul.

Utter madness giving advice such as has been given in this thread on an open forum.
Whats even worse is that some of you who pertain to be qualified & competent electricians think its fine to be giving unsound & potentialy dangerous advice on undertaking illegal work on the DNO supply/earthing side to anybody that cares to read the posts.
So now from this flawed advice any old diyer or new student to the trade, will think its common for us to illegaly tamper with the DNO earthing/sheathing. Well I can hand on heart say I've never used a 951 clamp on a TNS sheath.

I have however called DNO & had them out with in a 3 hour period to make good a poor connection, any longer & I'd have TT'd it as in my view it's safer for me to knock in a rod than tighten a clamp on a lead sheath that might be thin/cracked/bent/damaged internaly or I could just plain old tighten the screw to far.

Maybe DNO's refrain from letting us remove cutout fuses, because they see examples of incorrect advice given such as here.

I would advise any moderators to pull some of the unsound advice here.

Professionals my a.r.s.e
 
same problem i've got right now in my own home have just phoned dno and keep getting fobbed of. So from my connection get no reading but have a reading of the sheath, so not a good idea to put my own clamp on?
View attachment 5901

That looks like an old metal cut out.

The DNO in my area (NEDL) are changing one of these at one of my customer's houses as they are no longer permitted & they have to change them free of charge to the customer.

They have to dig a hole outside the house & chop the cable to isolate the metal cut out, fit a new plastec one then reconnect the cable & make good the hole.
 

Reply to Suppliers Earth TN-S in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
153
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
518
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
459

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top