Hi ,I have a wood cabin outside 70mtrs from house incoming supply, I was thinking of using a 35mm 2core pvc/swa, as I think a TT system would be appropriate for the cabin, owing to the distance away from house load would be allowing for diversity would be 51amps, seems a lot but it will be a live in dwelling with all requirements for cooking heating etc,am i correct with supply size Thanks ron
 
What's your installation method, earthing arrangement, bonding requirements?
 
PVC/SWA would be buried in the earth at appropriate at depth
my calcs as follows , volt drop table 4E4B 1.85mv/a/mt 35mm =1.35 x50ampsx70mtrs =4.72 volts . 25mm = 1.85mv/a/mt x50amp x70mtr= 6.47volts so not much lighting load so 5% of 230volt=11.5volts allowed and 3% of 230volt =6.9 volts so would the calc with 5% be okay which is 11.5 volts am I getting to tied up ronky
 
Your volt drop needs to take into account the circuits within the cabin not just the distribution circuit.
 

Reply to supply cable sizing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

  • Question
If your using 35mm or 50mm use 2 core SWA and use the armour as the earth, it'll cut down on price. I know people will comment on this but the...
Replies
10
Views
1K
  • Question
If it is TT then you can use the armour of any of them as CPC but will almost certainly need an up-front delay RCD at the sub-main feed point to...
Replies
5
Views
939

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top