been to a job today where a seperate fuseboard has been fitted to supply an 8.5kw shower the supply and load cables for this board are 6.0mm twin and earth, the shower fuseboard has a 32a mcb and an rcd main switch and labelled up shower only, the feed for the seperate fuse board (only room for the one circuit) is 6mm twin and earth direct from the main Fuseboard incoming terminals is this ok ? The main fuse is 60a as the load is fixed at 32a and the 6mm cable is suitable for this the run between consumer units is surface mounted and double insulated less that 300mm long the only protection for the 6mm cable feeding the seperate fuseboard is the main fuse 60a no overloading of this cable is possible as the upstream 32a mcb restricts this the only issue would be a short circuit should the cable be damaged which with the PFC reading 1.2ka this is irrelevant isn't it ? Just wondering, Or have I misunderstood
 
been to a job today where a seperate fuseboard has been fitted to supply an 8.5kw shower the supply and load cables for this board are 6.0mm twin and earth, the shower fuseboard has a 32a mcb and an rcd main switch and labelled up shower only, the feed for the seperate fuse board (only room for the one circuit) is 6mm twin and earth direct from the main Fuseboard incoming terminals is this ok ? The main fuse is 60a as the load is fixed at 32a and the 6mm cable is suitable for this the run between consumer units is surface mounted and double insulated less that 300mm long the only protection for the 6mm cable feeding the seperate fuseboard is the main fuse 60a no overloading of this cable is possible as the upstream 32a mcb restricts this the only issue would be a short circuit should the cable be damaged which with the PFC reading 1.2ka this is irrelevant isn't it ? Just wondering, Or have I misunderstood

If I read your post correctly the cables between the 60 amp cutout and the board are only 6sqmm. They have to be rated for 60 Amps whatever is downstream. In this case if Reference Method C, 2 single 10sqmm cables (tails) and a 10sqmm earth are required (assuming a PME supply). You could use 10mm T&E but run a seperate 10mm earth.
I would not connect these into the incoming terminals on the main board. It's messy and you run the risk of dodgy connections. I'd supply both boards from Henley Blocks.

Pete
 
If I read your post correctly the cables between the 60 amp cutout and the board are only 6sqmm. They have to be rated for 60 Amps whatever is downstream. In this case if Reference Method C, 2 single 10sqmm cables (tails) and a 10sqmm earth are required (assuming a PME supply). You could use 10mm T&E but run a seperate 10mm earth.
I would not connect these into the incoming terminals on the main board. It's messy and you run the risk of dodgy connections. I'd supply both boards from Henley Blocks.

Pete
6.0 tails are fine and if it is not supporting bonding so is 6.0 earthing conductor. The correct professional way to supply the shower is to replace the existing CU thus leaving a single means of isolation.
 
Can I say this install is dangerous, and condem it ? It's been like that for years and in my mind looks to be neatly installed and electrically sound if as in so many cases you class the main fuse as the main isolator all terminations sound and no risk of overload just unorthodox
 
Can I say this install is dangerous, and condem it ? It's been like that for years and in my mind looks to be neatly installed and electrically sound if as in so many cases you class the main fuse as the main isolator all terminations sound and no risk of overload just unorthodox
It probably isn't dangerous as you said been like it for years. You can't class the main fuse as isolation, the property should have a single point of isolation, it is a domestic property and there is no excuse for ad hoc additions.
 
It probably isn't dangerous as you said been like it for years. You can't class the main fuse as isolation, the property should have a single point of isolation, it is a domestic property and there is no excuse for ad hoc additions.

It just looks wrong then, there would there be no Issues had it been supplied from the load side of the switch then ?
 
It just looks wrong then, there would there be no Issues had it been supplied from the load side of the switch then ?

IET guidance note 2 says something along the lines of....A dwelling can have more than 1 electrical installation therefore one main switch is not required to isolate all consumer units simultaneously providing the consumer units have an integral main switch. Its a requirement that each device used for isolation to be clearly identified by positional or durable marking to indicate the installation it isolates. How ever the guidance notes are just that guidance and I agree its prudent to have a single point of isolation.
 
IET guidance note 2 says something along the lines of....A dwelling can have more than 1 electrical installation therefore one main switch is not required to isolate all consumer units simultaneously providing the consumer units have an integral main switch. Its a requirement that each device used for isolation to be clearly identified by positional or durable marking to indicate the installation it isolates. How ever the guidance notes are just that guidance and I agree its prudent to have a single point of isolation.
I would read this as different tariffs of supply like off peak. A dwelling isn't a large installation which may require more than one supply. To me no excuse in a dwelling.
 

Reply to Supply for shower board in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Merry Xmas to all :D
    • Friendly
    • Like
Replies
8
Views
411
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
743
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
408
I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
609

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top