I have installed this arrangement many times over the years and never had an issue with accumulated leakage on a domestic installation to that level.
I have however come across this issue on dairy installations where the vacuum pumps have been upgraded and changed to vfd driven. The vfd's were causing the milking shed to trip and shut the whole lot down!
Single pole rcbos with a N+E fault can take out the upfront S type.
I also came across where next doors' induction hob was tripping the up front s type in the other house.
 
Last edited:
Single pole rcbos with a N+E fault can take out the upfront S type.
I also came across where next doors' induction hob was tripping the up front s type in the other house.
That they can but that is not accumulated leakage, that is a fault.
Having double pole RCD's downstream of the main switch RCD limits that to a few circuits, now with double pole RCBO's this is much less of a problem.
 
That they can but that is not accumulated leakage, that is a fault.
Having double pole RCD's downstream of the main switch RCD limits that to a few circuits, now with double pole RCBO's this is much less of a problem.
The point being whether it’s a fault or accumulated leakage you can’t guarantee total selectivity using a up front rcd on a tt supply.
 
I've seen an upfront 30mA/100ms upfront RCD taken out when testing downstream RCBOs, although I'd consider that a fairly unusual situation. In the majority of domestic TT installations, any upfront Type S RCD would generally be 100mA - I doubt most wholesalers would stock any other single phase Type S RCD.
 
I've seen an upfront 30mA/100ms upfront RCD taken out when testing downstream RCBOs, although I'd consider that a fairly unusual situation. In the majority of domestic TT installations, any upfront Type S RCD would generally be 100mA - I doubt most wholesalers would stock any other single phase Type S RCD.
I agree but in most domestic situations they wouldn't be on a TT and if they are then they probably wouldn't have vfd driven borehole pumps, dual EV charging points, Solar, Wind, and battery storage :)
 

Reply to Supply Isolator required to be metal on TT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I would probably C3 it, based on no contact with sharp edges, all the terminations being tight, and no signs of any thermal damage. With all...
Replies
2
Views
803
View: https://www.youtube.com/watch?v=glsg2HpWyok
Replies
21
Views
616
  • Question
Underground or overground supply, there may well be a TNC-S earthing terminal provided in the service head, but the DNO might not give permission...
Replies
24
Views
2K
  • Question
There's some stunning Chinglish on that data plate
    • Optimistic
Replies
19
Views
2K
Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
488

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks