Had a customer today, kettle not boiling correctly, 4th replacement kettle in 3 weeks.
all not boiling past Luke warm
Supply characteristics
TT Supply 66ohms.
No Bonding as caravan and all utilities in plastic (caravan) bonded
RCD protecting caravan and caravan supply (30mA)
when kettle reaches Luke warm it stops boiling (but not click off) then temp drops and kettle brings water back to Luke warm
RCD: 9/15
PFC: 3.25
LN: 245v
LE:244v
NE: 1v
voltage drop: 3volts under load
anyone got any ideas? I am implied to say kettle but how can this be the 4th kettle in 3 weeks?
2nd and 3rd and 4th kettle never worked correctly. 1st worked for 2 weeks
tried different sockets at different locations through the site (garage, new build site supply, caravan)
all under same supply but different CU from same main ISO
Recommended customer to give to daughter to test (some 30miles away)
all not boiling past Luke warm
Supply characteristics
TT Supply 66ohms.
No Bonding as caravan and all utilities in plastic (caravan) bonded
RCD protecting caravan and caravan supply (30mA)
when kettle reaches Luke warm it stops boiling (but not click off) then temp drops and kettle brings water back to Luke warm
RCD: 9/15
PFC: 3.25
LN: 245v
LE:244v
NE: 1v
voltage drop: 3volts under load
anyone got any ideas? I am implied to say kettle but how can this be the 4th kettle in 3 weeks?
2nd and 3rd and 4th kettle never worked correctly. 1st worked for 2 weeks
tried different sockets at different locations through the site (garage, new build site supply, caravan)
all under same supply but different CU from same main ISO
Recommended customer to give to daughter to test (some 30miles away)