Hi Folks
Please post all your ideas and suggestions here so we only have one place to look
Thanks
Chris
Please post all your ideas and suggestions here so we only have one place to look
Thanks
Chris
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Supply to OUTBUILDINGS in the Australia area at ElectriciansForums.net
As the cable(buried) is supplying a special installation the supply cable therefore should be RCD protected.
If the supply cable is visible for its entire length does it still need RCD protection?
Anyone agree
I would have to disagree, Mr Black, no requirement for RCD protection of the cable if mechanically protected. (e.g. SWA), unless an RCD was required for earth fault protection to meet EFLI maximums.
I'll start it off, then.
Contrary to some popular urban myths, there is no requirement for a seperate earthing system (e.g. TT/Earth Rod) at the outbuilding, regardless of the earthing system of the main installation.
The only thing that needs to be taken into consideration is the presence of extraneous conductive parts in the outbuilding and, if required, the CSA of the' Protective Bonding Conductor' that will need to be run along with the supply to the outbuilding.
The option is there to install an earth rod, should this be an easier and more cost effective option.
You then need to seperate your outbuilding earthing system from the main installation earthing system.
The feed to the outbuilding would be earthed at the supply end only.
That should get things rolling
If you mean that the supply cable should be protected by an RCD then absolutey my good man.Very important as some spark may come along at a later date and decide the outhouse needs a earth spike,fires it into the ground and ouch ouch what happened there..
Reply to Supply to OUTBUILDINGS in the Australia area at ElectriciansForums.net