Discuss Supply to OUTBUILDINGS in the Australia area at ElectriciansForums.net
I know the outhouse isn't a Special Location it comes under SPECIAL INSTALLATION there is a difference!!!!!!!!!!!!!!!!!!!!!
Check in the PART P DOCUMENT.Then tell me what you think.
Not sure what the relevance of this is. Part P is about what work is notifiable.....Bs 7671 determines how that work is carried out,not part P. In Bs 7671 a garden outbuilding is not a special location and therefore only the general requirements of Bs 7671 apply.
Hi again,
I'll probably post some more info from it when I get a minute Hope it helps.
I was asking a lecturer today about this today - he teaches the 17th wiring regs (and really knows his stuff) and it was his opinion that any shed/outbuilding outside the main building's equipotential zone should have its own earthing system, ie an earth rod.
Hi mate,
a lot of people have got this idea that you have to TT an outbuilding, but it's all rumour.
hence the expression 'drove a rod in for good measure'. When I hear that it just sounds like that person is unsure.
I agree, mate.
The funny thing is, by rodding the outbuilding, you are probably giving it a worse earthing system (i.e. Ze/Ra) than you would be by using the supply earth
nice picture.
where would you terminate the cpc going to building 2?
just says insulated from building 2 earthing arrangement.
cheers
Hi mate,
You should get him to have a read of GN8 then mate, coz he's got it wrong
I'm not criticising him, by the way, a lot of people have got this idea that you have to TT an outbuilding, but it's all rumour.
There may be some circumstances where it would make more sense to TT it, but that's a judgement call by the sparky on the job.
The other thing worth mentioning is that, if there are no extraneous conductive parts in the outbuilding, and therefore no bonding requirements, then you can simply run your SWA supply to the outbuilding, utilising either the armour, or a third core, as the CPC - once again, regardless of the type of earthing system of the main installation.
Hi mate,
You should get him to have a read of GN8 then mate, coz he's got it wrong
I'm not criticising him, by the way, a lot of people have got this idea that you have to TT an outbuilding, but it's all rumour.
There may be some circumstances where it would make more sense to TT it, but that's a judgement call by the sparky on the job.
The other thing worth mentioning is that, if there are no extraneous conductive parts in the outbuilding, and therefore no bonding requirements, then you can simply run your SWA supply to the outbuilding, utilising either the armour, or a third core, as the CPC - once again, regardless of the type of earthing system of the main installation.
On a subject like this full of Grey areas, we need to define what 7671 says, as thats the law. After that, we need to find out what our individual governing bodies state.Best practices etc. As its for those reasons that opinions differ so greatly. So if we can define what we say by quoting a reg, or say I do this, etc, because I believe its best practice etc, that would help.
I personally have followed my" master" and will rod the lot if I get a chance to prevent transporting a fault. It is time to move on from that as I have learnt from this forum, to develop my own methods.
If the outbuilding has extraneous metal parts such as a metal sink - then TT it and don´t use the TNCS earth from the main building. If the outbuilding doesn´t have extraneous metal parts then use the TNCS earth.