SWA armour supply to outbuilding, what CSA cable? and Reference Method?

Hi guys,

I am running a supply to an outbuilding that requires a 22m run from the Main CU (in the garage) to the CU in the outbuilding, at the Main CU it will be a 40A MCB supplying an 63ma RCD protected sub board which will then supply:

6A type B MCB for 12 downlights and an extractor fan
32A type B MCB for 3 double sockets
20A type B MCB for a 3.5kw split air condition unit

I've calculated the voltage drop if using 6mm 3 core SWA clipped direct (table 4E4A p372 BS 7671) 53 x 40A x 22m / 1000 = 46.64 Vdrop .. thats a crazy figure

And the supply will be feeding a sub board initially based on what I've been taught I calculated maximum demand by adding the breakers amp size and x them by 40% so 6+32+20 x 40% = 23.2A

The SWA will run up the outside wall from the garage into the loft and out the other end, and down galvanised conduit, into the ground and into and up a wall with insulation (2m) and into the outbuilding

The queries I have are:

The majority of the run will be clipped direct and only a small part of the length will be in insulated brick wall am I right/wrong to assume Reference method C (clipped direct)?

And as it is SINGLE PHASE 3 CORE cable I'm using I'm a little confused as the only two options under clipped direct in table 4E4A (p372 BS 7671)is '3 CORE 3 phase AC' and '1 two core cable SINGLE PHASE AC' my installation does not fall perfectly into either option, which should I select?

And how best would you recommend lowering the Voltage drop to the stipulated 5% 11.5V?


Thank you in advance for helping,

Mark
 
If the description of single phase or three phase phase wasnt obvious enough then consider that you will only be using two of those three cores that you have, therefore treat it as a two core cable. The ccc tables are only concerned with the cores which are carrying current under normal conditions for, what are hopefully, obvious reasons.

Do not use the values from table 4e4a for the voltage drop calculation, that table details the current carrying capacity of the cable. Use the values from table 4e4b on the following page which is clearly identified as being the table of values of voltage drop per ampere per metre.
 
Is this calculated in a different way? apologies for the nativity of the question.

The calculations are the same, its your metnod which is wrong.

Your apologies are irrelevant, you should have finished making this kind of mistake before you started dsigning circuits for the real world without supervision.

Trusting to a bunch of strangers on the internet will almost certainly invalidate your insurance and not be a valid defence in court should it all go wrong.
 
Taking pity...a few hints.
This is a distribution circuit. Therefore if you calculate allowing for the maximum volt drop on the distribution circuit only that will not allow for volt drop on any final circuits connected to the distribution circuit.
You also need to take into account that where a lighting load is to be supplied the maximum permitted volt drop requirement is not 5%.
Refer to App 12.
 
Last edited by a moderator:
I've calculated the voltage drop if using 6mm 3 core SWA clipped direct (table 4E4A p372 BS 7671) 53 x 40A x 22m / 1000 = 46.64 Vdrop .. thats a crazy figure

where did 53 come from.? the mV/A/m for 6mm is 7. so:

( 7 x 40 x 22 ) /1000 = 6.16.
 
I've calculated the voltage drop if using 6mm 3 core SWA clipped direct (table 4E4A p372 BS 7671) 53 x 40A x 22m / 1000 = 46.64 Vdrop .. thats a crazy figure

where did 53 come from.? the mV/A/m for 6mm is 7. so:

( 7 x 40 x 22 ) /1000 = 6.16.

He's used the CCC for 3 or 4 core 6.0mm from table 4E4A....53a!
That would rather skew the result.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
Sparky_marky2,
Last reply from
Richard Burns,
Replies
55
Views
11,871

Advert

Back
Top