SWA fault. | on ElectriciansForums
Discuss SWA fault. in the UK Electrical Forum area at ElectriciansForums.net
telectrix
Mentor
Nearly Esteemed
cheshire/staffordshire
never seen anything like this before. new cable supplied by cient, installed by ne. no probs. 2 weeks later get a call.. no power. continuity test proves brown conductor is o/c. client is in a catch22. has to return cable for replacement involving me 2 call-outs.... as a temp. measure, i rejigged it, using grey as L, BK as N, and armour as sole cpc. 8 wweks down the line, call to MCB tripped and won't reset. this is what i found after dissing the SWA completely.
[ElectriciansForums.net] SWA fault.cable was laid on ground prior to client digging trench, no chance of external damage. any ideas, apart from faulty manufacture?
Your avatar was hungry...
Seriously though that looks like its had something drive over it as there is clear evidence of punctures in the outer insulation caused by the stones maybe which has allowed it to tear?
cable laid on stones, almost under a hedge. no spades, no traffic. and, after the 1st problem with the brown o/c, no visible signs of damage. and today, no signs of crushing due to a spade.
can virtually state that the cable has not been touched or tampered with. it's a pikey site with caravan hook-ups. pikeys might not be the most intelligent of the species, but they don't try to nick their own stuff.
Right get you now, not a Pikey gang war going on? trying to cut off their supply (electric supply I mean)
when 1 conductror goes O/C, and IR tests confirm the other 2 and the armour, then i have to assume a manufacturing fault. having rejigged it to get power back on, then have this failure 2 months later, i have to assume a cable fault.
Reply to SWA fault. in the UK Electrical Forum area at ElectriciansForums.net