Up until now every installation I've worked on has involved the C.U being within 3m of the supply.

The job I'm working on at the moment is a domestic rewire that has had the supply moved to a box on the outside of the property, and the new C.U will be in a utility room about 4 - 5m away from the supply.

The supply is TN-S with a BS 1361 100 a main fuse fitted. What I'm planning on doing is installing a metal clad 80 A switch fuse at the supply. The customer has already had a 2 core 25mm SWA cable run from the supply box to the new C.U location.

No separate Main Earth has been run with the SWA to the new C.U position though which is my main concern - though after doing some research it seems to be indicated that using the steel armour of the SWA as the main earth should be fine so long as it's PVC SWA (PDF linked below has a useful table):

http://www.earthingnuts.co.uk/pdf/pvc_xlpe.pdf

If anyone here has experience with this and could confirm either way that'd be great.

If it is compliant, my next question would be how to correctly terminate either end of the SWA to the MET and C.U Earthing terminal - I'm thinking of using a banjo along with a couple of short lengths of 16mm.

EZ.
 

Reply to SWA from supply to C.U questions in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
489
You would treat it as a TT installation.
2
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top